Zones and sockets | on ElectriciansForums

Discuss Zones and sockets in the UK Electrical Forum area at ElectriciansForums.net

timhoward

-
Broke Internet
Esteemed
Arms
Supporter
Joined
Jul 19, 2019
Messages
4,623
Solutions
1
Reaction score
9,346
Location
Oswestry
Regarding the "sockets allowed 3m horizontally from the boundary of zone 1" reg...something I've never had to consider before as most UK bathrooms wouldn't be big enough!

Looking at this plan from OSG
[ElectriciansForums.net] Zones and sockets


Does the 3m only apply in the direction of my red arrow, or does it arc around in the same way Zone 2 does?
And getting the the point, does the partition mean a socket in position marked X is ok at any distance, or is 3m from the green dot needed?
Thanking you!
 
in 701 it says (as you know) socket outlets prohibited within 3m horizontal from boundary of zone one.. so I would suggest as they show your green dot as the boundary to get from zone 1 to zone 2 at the 0.6M, it would follow as the reference point for the 3m for the ‘boundary of zone 1’ so an arc of 3m from the green dot.
 
in 701 it says (as you know) socket outlets prohibited within 3m horizontal from boundary of zone one.. so I would suggest as they show your green dot as the boundary to get from zone 1 to zone 2 at the 0.6M, it would follow as the reference point for the 3m for the ‘boundary of zone 1’ so an arc of 3m from the green dot.
Thanks that was my assumption too, this is going to an interesting one as a kitchen is in middle of conversion to shower room and client has fallen out with builder. More details later!
 
in 701 it says (as you know) socket outlets prohibited within 3m horizontal from boundary of zone one.. so I would suggest as they show your green dot as the boundary to get from zone 1 to zone 2 at the 0.6M, it would follow as the reference point for the 3m for the ‘boundary of zone 1’ so an arc of 3m from the green dot.
Technically I'd agree, but the interesting bit about this particular application is that the shower cubicle has a partition wall where the arc of the zone is located. For zone 2 this would make sense as a person could reach around. But on appearance this partion (which I assume is floor to wall) reduces access & water ingress significantly.
 
Technically I'd agree, but the interesting bit about this particular application is that the shower cubicle has a partition wall where the arc of the zone is located. For zone 2 this would make sense as a person could reach around. But on appearance this partion (which I assume is floor to wall) reduces access & water ingress significantly.
Maybe so, but we're not talking about the distance a person can reach while standing in the bath/shower, as obviously 3m is way beyond arm's reach. The 3m rule takes into account the length of the appliance cord.

So I agree with the arc from the green dot applying to 3m for a socket.
 
Maybe so, but we're not talking about the distance a person can reach while standing in the bath/shower, as obviously 3m is way beyond arm's reach. The 3m rule takes into account the length of the appliance cord.

So I agree with the arc from the green dot applying to 3m for a socket.
Yeah good point.
 
Extend the partition by the shower slightly, then fit a door frame and door, hinged on the wall by the red arrow. The shower tray and the small space in front of it then becomes the 'room with a bath or shower' and the rest of the room is then exempt from this stupid 3m regulation. Regs. don't say anything about the door of the 'room with a bath or shower' being closed, so can be left permanently open against the wall.
Door frame doesn't need a top, and the open door can be repurposed as a shelving unit.
 
When I went to look at this job the shower had not been dreamt up. From memory there are a number of interesting things to check, as there's also a combi boiler with spur and at least a couple of sockets. I'd imagine the spur will be out of zones.
There's also a consumer unit the other end of the room, and I'm not loving the idea of that being in a steamy room, albeit with extractor fan. External influences and all that....
So this whole job needs another visit and a careful think.
Thanks for the responses, and Brian I'll keep that one up my sleeve!!
 

Reply to Zones and sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
1K
  • Question
Quinetic switches are your friend here!
Replies
12
Views
2K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
  • Question
Single Pole, Single Pole Switched Neutral, and Double Pole are all different things. Hager RCBO's are Single Pole. I was recommending Single Pole...
Replies
33
Views
5K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks