This is in conjunction with an EICR I have just carried out.

9.5kW shower on 6mm and 32A MCB. Been in place for a long time, no signs of thermal damage in CU or 45A shower pull switch. Ref method C (where visible in loft), unable to clarify ref method where it is buried in walls, but no conduit visible. My thoughts.... No code, but I am unsure of the effect of 41A going through a 32A MCB over a long period of time? Will this eventually damage the MCB or have some other effect on it that may compromise it's ability to work as it should, and if so, is this a very unlikely occurrence that doesn't really need to be considered or the opposite?

No 30mA RCD on cable <50mm in walls (for 3 x circuits... cooker, water heater, lights).
No 30mA RCD for circuits running through/in special location
Main bonding in place, nothing to supplementary bond.
My thoughts.. I have always put C3. I still think C3, but I am starting to err towards C2 in general for no RCD. This is for 2 reasons, RCD's are now required for pretty much everything (and they save lives), secondly, does anyone know what the NAPIT codebreakers says about no RCD protection? I believe they say C2?

Cheers all.
 
My take - for the shower the 32A breaker probably protects the 6mm T+E cable adequately, and there's a higher fixed load on the end that for a long time has proved not to cause tripping with no signs of thermal damage. So the first one isn't a biggie for me. No code, or C3 for new cable ideally required. MCB's are generally fairly resilient and you've checked the isolator too.

Regarding RCD protection - are any of the sockets likely or available to be used outside?
If not, you could construct a BPG4 argument that they are C3's.
You could construct a Codebreakers argument they are C2's:
1623841610588.png
You could also construct an "I'm the inspector and it's about time this rental had at least one RCD" argument too if you so chose, I'd normally chat with the landlord and see how reasonable they are - I prefer it to be mutually agreed than just code it C2 as it isn't potentially dangerous in a clear cut way.
I'm assuming it's a rental - might not be!
 
My take - for the shower the 32A breaker probably protects the 6mm T+E cable adequately, and there's a higher fixed load on the end that for a long time has proved not to cause tripping with no signs of thermal damage. So the first one isn't a biggie for me. No code, or C3 for new cable ideally required. MCB's are generally fairly resilient and you've checked the isolator too.

Regarding RCD protection - are any of the sockets likely or available to be used outside?
If not, you could construct a BPG4 argument that they are C3's.
You could construct a Codebreakers argument they are C2's:
View attachment 86772
You could also construct an "I'm the inspector and it's about time this rental had at least one RCD" argument too if you so chose, I'd normally chat with the landlord and see how reasonable they are - I prefer it to be mutually agreed than just code it C2 as it isn't potentially dangerous in a clear cut way.
I'm assuming it's a rental - might not be!
Cheers Tim.
Have you got the NAPIT code breakers book? Just wondering where you got the picture from? I'm guessing you have to pay, even if a NAPIT member, or is there a cheeky link somewhere.
 
Cheers Tim.
Have you got the NAPIT code breakers book? Just wondering where you got the picture from? I'm guessing you have to pay, even if a NAPIT member, or is there a cheeky link somewhere.
Hi
No, as a NAPIT member I probably shouldn't admit that I don't have it! I prefer to work to BPG4 in all honesty.
That picture came from a NAPIT article I received.
Codebreakers is about £20 btw.
Tim
 
No RCD but supp bonding in place I would C3.

I would C3 the shower size as there's no sign of thermal damage etc, and I would strongly recommend to the customer that it is either replaced or the MCB and cable replaced. Long term the MCB will start to either nuisance trip or even worse fail to operate when needed.
 
up the MCB to 40A on shower. otherwise a C3. you can't tell if that 32A has been stressed running at (>) max. rated
 
No RCD but supp bonding in place I would C3.

I would C3 the shower size as there's no sign of thermal damage etc, and I would strongly recommend to the customer that it is either replaced or the MCB and cable replaced. Long term the MCB will start to either nuisance trip or even worse fail to operate when needed.
Both options for the shower would result in it being safe, but both would be pretty expensive. Perhaps a better option would be to 'FI' it? Actually take a floorboard up, see where it goes up the first floor wall to the loft and take a bit out of the wall to see how it is routed. A bit messy, but probably cheaper than changing the shower or cable, as it's likely it'll end up as ref method C.
 
Another what code!

This is in conjunction with an EICR I have just carried out.

9.5kW shower on 6mm and 32A MCB. Been in place for a long time, no signs of thermal damage in CU or 45A shower pull switch. Ref method C (where visible in loft), unable to clarify ref method where it is buried in walls, but no conduit visible. My thoughts.... No code, but I am unsure of the effect of 41A going through a 32A MCB over a long period of time? Will this eventually damage the MCB or have some other effect on it that may compromise it's ability to work as it should, and if so, is this a very unlikely occurrence that doesn't really need to be considered or the opposite?

No 30mA RCD on cable <50mm in walls (for 3 x circuits... cooker, water heater, lights).
No 30mA RCD for circuits running through/in special location
Main bonding in place, nothing to supplementary bond.
My thoughts.. I have always put C3. I still think C3, but I am starting to err towards C2 in general for no RCD. This is for 2 reasons, RCD's are now required for pretty much everything (and they save lives), secondly, does anyone know what the NAPIT codebreakers says about no RCD protection? I believe they say C2?

Cheers all.
@HappyHippyDad , have a read of this similar thread I posted a while back, there is some input from the manufacturers there too which is interesting:


FWIW, I recon I see this arrangement (6mm/32A MCB, with shower pulling >32A) more often that I see correctly installed shower circuits. I have yet to find it having obviously damaged the MCB, and have only come across it causing nuisance tripping once (old 30A plug-in BS3871, 8.5kW shower IIRC). I usually award it a C3.

For a shower without RCD protection I give a C2, regardless of sup bonding. Shower manufacturers always state that they need RCD, and I am led to believe that has been the case for quite a while now (>15 years).
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
-
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What code for this?