Moved into a new house and before I make a start on the serious renovation, thought I'd mount a TV so I have some evening entertainment.

Easy, the previous owners already had one up, just need to move along slightly for new pilot holes for the new bracket. Or so I thought.

Drilled first pilot hole, no issue.
Drilled second pilot hole and lights in room went out. (I didn't connect the two immediately as the microwave was on and this earlier triggered the RCBO).
Drilled third pilot hole and poof, bit of a spark, RCBO triggered again and told me something was not right.

The things that are alarming me are:

1) I've drilled a couple of inches horizontally from where previous mount was installed. Closer to a power socket but nowhere near above. Further away from a light switch and in no logical route of a cable run

2) the room lights are switching off when there was a power overload earlier on the sockets. Don't know why these would be on same RCBO.

This house is completely new to me less than a week ago so don't have a full understanding of the electrics but there s growing number of warning signs that something isn't right
 
I'm not up to speed with my corporate logos, there is no name visible but this logo on the CU coverView attachment 86736
The board is Lewden as well, so breakers and board are matching. Just looks like they don’t fit very well.
 
The board is Lewden as well, so breakers and board are matching. Just looks like they don’t fit very well.
Suspect a case of not fitted well ie more user than product error ?? I continue to find shockers. Found the coax collection point with two random T&E open terminated into one half of a choc box (ie stick anything in the other side and bam!). By the sheer number of fused spurs this is definitely a property that has had its electrics added to over the years as opposed to a full rewire.
 
For completeness for anyone that pulls up this thread years to come. Have completed the fix. If it was in any other location I would have preferred to rerun a whole new cable but with the existing wires clipped to the outside of the original property and no obvious channel to use, I had to settle for crimping, heat wrap and tape (tucked in temporarily for now)
[ElectriciansForums.net] Made me jump!
[ElectriciansForums.net] Made me jump!
 
( tricky I would be tempted to leave - a note of location of repair for if any future readings are a bit off )
Gives you an clue of an area to thump to see if anything missbehaves.!
I have been guilty of putting a note inside a coax junction box before now, whether any one ever see's it or not I don't know, or a sticky label on a hidden socket behind the TV may work.
 
Good eyes. It has just about but not penetrated inner sheath. Is that good to leave or is there anything I can do aside from cut out and repair?
View attachment 86768


Note, I've put my tin hat on.

I'd wrap a couple of layers of tape around it neatly. That's assuming the damage has definitely not gone right through the outer sheathing.
 
Note, I've put my tin hat on.

I'd wrap a couple of layers of tape around it neatly. That's assuming the damage has definitely not gone right through the outer sheathing.
Tis what I'm thinking and tin hat is right ? is there anything I should mark on the tape to let a future electrician know why it's been taped or just not the done thing?
 
I would skin up a 150mm length of the outer sheath of a 16mm swa cable and fix that over it.

But I'm no electrician so could be speaking out of my backside ?
 
If there is enough slack in the cable I would be tempted to do the same as you have to the others, but that's me, belt and braces.

I knew you'd go that way Mike. Be interesting to see what the general consensus is.

I accept my way is technically a bodge, but I think it's acceptable. Again, with my tin hat on. It avoids several joints which are potential failure points.
 
Thank you all. I will go the tape route, acknowledging it's not the ideal treatment but one as the property owner am happy with but also know that no-one is drilling into that wall for the next 50 years as I plan to die in this house :)

To complete the loop, the TV is now mounted on the wall and all working fine. I've completed the coax routing check around the house with the aid of a great little (and cheap) device from Klein tools (https://www.amazon.co.uk/gp/product/B076DP1534/ref=ppx_yo_dt_b_asin_image_o08_s01?ie=UTF8&psc=1)

Next on the to do list is to check all the CAT5/6 terminals although I've already come across helpful labelling such as "does not work" :) :)

Oh...and my wall scanner arrived so hopefully no more crimping (famous last words)
 
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.
Right...so I've got a cable route which has some coax, ethernet and these two random white cables with brown and blue wires terminated in a chocbox.

For life of me can't figure out why they were routed there or what they do. Anyone have a guess where they may be routed near a TV location? Hopefully can use that information to figure out where they end up as haven't found the other side yet!

[ElectriciansForums.net] Made me jump!
[ElectriciansForums.net] Made me jump!
 
I assume the two co-axial cables are from a dual LNB from a satellite dish to allow signal to a receiver box and allow one programme to be recoded whilst watching a different programme, can't help on the two white cables, perhaps low power cables? have you checked if power is supplied to them?
 

Reply to Made me jump! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
641
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
You too? I thought I was in a unique position:anguished::coldsweat:
    • Like
Replies
5
Views
222
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
291

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks