Evening all.
Doing a EICR in a rental today and presented with this.
installation date is 1992 and there seems to be no records since.
At some point in the recent past someone has added a electric shower circuit. Obviously a smash and grab merchant as no earth sleeve and it was the same in the pull switch.
The 32a MCB is the shower. Now I know a circuit supplying a location containing a bath or shower with no RCD is a C3
But something is irking me that with this being the shower itself then it should have a RCD so I am leaning to a C2. However I can’t seem to find anything to support that.
Before I go slapping an unsatisfactory on the EICR thought I’d garner option on here.
Ta in advance.
Raptor