Hi,what code would you give gor this light in a bathroom.Please see photo.Thank you in advance for the answer.
 

Attachments

  • [ElectriciansForums.net] Hi,what EICR code would you give for pendant light in a bathroom
    16256966252845905216797903427665.jpg
    221.2 KB · Views: 33
Best Practice Guide suggests C2 where a light is not IP rated and may be dangerous, or C3 where it is not immediately dangerous.

I'd go C2 on that, as it looks like it's nearly in zone 1 - though that does depend on the height - if it's above 225cm then it's outside zones anyway so can only be C3.

I assume there's a shower somewhere? Is it one that could be pointed at the light, accidentally or otherwise? that's would make it a definite C2 for me I think, even if it's RCD protected...

If there's not shower then I'd consider it a C2.5 - probably been there with no issues for years, but needs to be fixed....
 
If you can reach it will standing in the bath C2 , if it’s out of reach then check it is above 2.25m then no code

never quite understand why an electrician would fit a batton lamp holder in a bathroom
 
If it were inside zone 2 it would still fail because the shock guard isn’t IP44.
Apologies, posted pre coffee.
I hadn't read the thread properly and assumed it was a re-run of the 'But you might change the bulb while naked and standing on the edge of the bath.' argument.
As above the guidance on what kind of fittings can go where in a bathroom is clear and abundant.

OSG, and BPG 4 and of course the BBB amongst others.
 
Thanks for all the replies,just one more thing at the time of fitting that batten was not against any regs probably so my question is does it have to be upgraded,I mean situation with all the plastic consumer units,they do not have to be upgraded to metal ones unless you change them anyway,you just can not install another plastic one.Once again thanks for answers.
 
When I first started, it was the preferred lamp fitting for a bathroom, but had to be fitted with a ' HO skirt', which is probably similar to the 'shockguard' one. Pendants were not allowed, and little else was available.
Although legal when installed, I doubt if a shower of any kind was present then, and on that basis, that conditions have changed, I'd code it C2 if it's in zone 2. If it's not in zone 2, you can note it and recommend that it's changed, but you cannot give a coding that makes the installation "unsatisfactory".
Curiously, If it's in zone 2 with a lamp fitted, it's almost certainly outside of the zones if you remove the lamp.
 
never quite understand why an electrician would fit a batton lamp holder in a bathroom
A lot of bathrooms never had showers when they were originally built, hence the name bathroom. And dependant on which version of BS7671 there were designed and installed to then zones may not have even been in existence.
 
then zones may not have even been in existence.
I still think of bathroom zones as something relatively new!
The 'old' wording was " not in reach of a person using a bath or shower" (which is further than zone 2), but IIRC, only applied to switches. I don't think lamps were mentioned, although 'common sense' was expected back in the dy.
 

Reply to Hi,what EICR code would you give for pendant light in a bathroom in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

It was purely an off the top of my head example, but I'd say - accessible live parts C1 - inaccessible live parts C2 - 10 feet up in a locked room...
Replies
9
Views
718
It’s difficult to advise on an electrical issue when some isn’t very conversant with electrical terminology.
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top