3 Phase RCD? | on ElectriciansForums
Discuss 3 Phase RCD? in the UK Electrical Forum area at ElectriciansForums.net
Scotland
I have recently started on a site where there is a 16A 3 phase Atex socket which is supplied by a 16A 3 phase MCB. It was picked up on a recent inspection that it needs an RCD. For the life of me I cannot find a 16A 3 phase RCD. I started to think does it really need an RCD? The socket is only used for one piece of equipment which is regularly maintained and only used by trained operators. The building in which the socket is in is not used very often as it is a warehouse and power is off to the socket when the building isn’t occupied.
Any advice greatly appreciated
[ElectriciansForums.net] 3 Phase RCD?
found in 30 seconds.
Are you looking for an RCD or RCBO? If RCBO then Tel has found you an example above. If you just want an RCD to use downstream of the existing 16A MCB then a 25A or 40A device will be much more readily available and probably cheaper.
Would it be possible to remove the socket and replace it with an isolator, thus removing the requirement for RCD protection?
A risk assessment would have to show a good reason why an RCD is not required in this case, documented and attached to the existing certification.
The Napit Codebreakers book has a whole 18 page chapter on the subject of risk assessments for the omission of RCDs:
Used 25, 40 and 63 amp 3 phase RCDs and then fitted fused switched isolators after the RCD so can downgrade to suit. This was in oil and gas industry too setting up life testing in workshops and also on sites.
Needs to be a socket as the equipment does get moved about. Thanks for the info much appreciated
Here’s a thing about those particular RCBOs….. the 4p neutral is just a dummy. So what that means is that inside a 3ph board you end up ‘losing’ 2 adjacent phases if you’re only populating with 3ph devices. AND - as I found to my distress on a recent job, they only do that on the right hand side - on the LEFT bus you end up with the N as L1 which means when you come to present cable you end with Blk-Gry-Brown, miss two, and it just looks so wrong!! ?
Reply to 3 Phase RCD? in the UK Electrical Forum area at ElectriciansForums.net
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
the manufacturer's instructions may specify an rcd must be fitted but other than that, your plan seems sound to me.
5K