I'm doing some calcs for college and need a little help.

So, Iz has to be greater than In, but I'm not achieving this.

My totals watts for a lighting circuit is 354w

So 354/230=1.54

Ib=1.54A

In=6A for lighting CPD

Correction factors of:-

Ca - 0.91
Cg - 0.7

Iz = 1.54/(0.91x0.7) = 2.4A

What do I do?

Cheers
 
You have worked out the current, you now need to select the correct cable and protective device.

Looks like you're getting confused, Iz is current carrying capacity, In is the current setting of protective device.

You have calculated Ib which is the design current.
 
Are you getting a little confused between Iz and It. Page 333 of BS 7671 equation 2 states to work out the value of It you divide In by the correction factors. In your calculation you divided Ib by the correction factors. By using In you will always satisfy the requirements of regulation 433.1.1 of BS 7671.
 
I have picked the protective device at 6A MCB and 1.5mm cable

How did you select the cable size without completing the cable size calculation?

You’ve divided Ib by the de rating factors where you should be dividing In by the de rating factors.
So It=In/(Ca.Cg)
Once you have done that you can use Iz to select your cable size from the tables.

It’s also worth noting that It doesn’t necessarily have to be greater than In, the rating factor Ca for example can be greater than 1 for low temperatures so can result in a lower It than In.
 
At college I've always been taught that Iz=Ib/Cg x Ca

This is an example of what we do...attached

Then I’m afraid to say you may have misunderstood, or your college are teaching you incorrectly.
It can be calculated by this method if overload protection is not required, but not Iz

Iz is the current carrying capacity of a cable, this can be calculated by multiplying the tabulated current carrying capacity by the rating factors. This is explained in the appendix to the regulations along with the reasoning for why we rarely carry out this calculation, normally It is calculated to establish the required conductor size.
It should be greater than or equal to In divided by the rating factors.
 
hi there everyone this is my first post here so be patience whit me.. Im doing the electric course and im doing my assessment and in need of some help.
for my understand iz=in/CaxCgxCi......
then it is from the tables 4D2A Correct?
on the images I add I did some of the calculations but I start to think im doing something wrong. can you clarify it for my.. like do I need to fill the iz when im doing a ring final?
Thanks for help...
 

Attachments

  • [ElectriciansForums.net] Iz not greater than In
    IMG_0620.JPG
    255.6 KB · Views: 148
  • [ElectriciansForums.net] Iz not greater than In
    IMG_0621.JPG
    210.6 KB · Views: 104
  • [ElectriciansForums.net] Iz not greater than In
    IMG_0622.JPG
    230.9 KB · Views: 111

Reply to Iz not greater than In in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
1K
  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
618

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top