saint elmo
Trainee
hi im redoing the bathroom and the 9.5kw shower is on this cable which has burnt at the connector block at some point its on a B32 MCB
im not sure what size this cable is, measuring the cable width it looks to be 6mm2 measuring the conductor looks to be a 10mm2
the diameter of the individual conductors is between 4-5mm
the width of the overall cable is about 14mm
the earth is significantly smaller, slightly thicker than a 2.5mm2 conductor
pictured next to 2.5mm2 cable for comparison
when i put everything through the IEC calculator it says the earth size should be the same as live and neutral cable wrong anyway?