Hello. I bought an old three phase compressor but it has come without a starter switch. Just five cables, two for the pressure switch and three for the three phases.

I have a DOL starter switch, but I don't know how to wire it to make the compressor come on and off with the pressure switch. Obviously my phases gonon T1, T2 and T3. But the pressure switch, where would that go to make the compressor automatically start and stop as it goes open and closed circuit? I have a wiring diagram I was supplied with but wanted to ask real professionals before jumping in.

Thanks in advance


[ElectriciansForums.net] 3 phase compressor DOL wiring


[ElectriciansForums.net] 3 phase compressor DOL wiring
 
Remove the existing red wires, then wire it exactly as the diagram, it will start and stop according to the pressure.

The start/stop on the starter will no longer work, so you must add an isolator rated for the full motor rating ahead of the starter to isolate it.

There are ways to add an emergency stop button, but to do it properly you need a second contactor so it locks out.
 
Just here? Unlabelled terminals at the bottom?

Really appreciate the help. I'm glad I didn't jump in, I'd assumed the pressure switch went between 96 and 14.

Thanks again. I have an isolator switch, an EM stop will be fitted too.

Shame it can't be made to work with both the buttons and the pressure switch. Oh well!


[ElectriciansForums.net] 3 phase compressor DOL wiring
 
Just here? Unlabelled terminals at the bottom?

Really appreciate the help. I'm glad I didn't jump in, I'd assumed the pressure switch went between 96 and 14.

Thanks again. I have an isolator switch, an EM stop will be fitted too.

Shame it can't be made to work with both the buttons and the pressure switch. Oh well!


View attachment 88323
Yes, I imagine they are marked somewhere
 
The point being that the contactor either has to latch the state of the buttons (i.e. whether the start or stop button was the most recently pressed) or follow the position of the pressure switch. One contactor can't do both.

If the unit requires an unloading valve and the valve is built into the pressure switch, and the pressure switch has a manual control, then you should preferably start and stop the unit with the pressure switch manual control. Otherwise if you stop the motor using a separate manual switch or button while running, the unloading valve won't operate and depending on how good the N/R valves are it might take a while before it can be restarted without stalling the motor.
 

Reply to 3 phase compressor DOL wiring in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Here are the other drawings
    • Optimistic
    • Funny
Replies
6
Views
1K
  • Question
That looks like a Metrel display (I have one), they have a permanent 3 wire display that measures the three combinations so I would say that’s a...
Replies
5
Views
644
Thanks for the advice. I'm going to look for a electrician to come over and do this. Better safe than sorry.
Replies
2
Views
832
When I was on the electric board We had a pair of pillocks connect a housing estate to a very large genset, the n lead was in two parts and not...
2
Replies
28
Views
3K
  • Question
Am I missing something here? motor is 690/400v you have a single phase 230v supply. every single phase vfd I have Come across has no way of...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks