Can someone please tell me why there new thermostat isn't powering up? I copied the wiring from the old one, with the exception of the earth wire, which I have capped in a wago. Thank you.
[ElectriciansForums.net] Wiring a new smart thermostat
[ElectriciansForums.net] Wiring a new smart thermostat
[ElectriciansForums.net] Wiring a new smart thermostat
[ElectriciansForums.net] Wiring a new smart thermostat
[ElectriciansForums.net] Wiring a new smart thermostat
 
Looks like you need a permanent live in terminal 4, a neutral in terminal 3 then 1&2 are the switch contacts for the heating system. Do you have a neutral at that stat? It looks like there may be but would need to test to be sure!
 
your new stat requires a L to terminal 4 and neutral to terminal #3. the relay is 1& 2. depending on whether you want to switch 24V or 240V, you may not have enough conductors.
 
Most stats are wired like that, it looks like you have enough cores there if the boiler control circuit is 230v! You will need to test to find which is live, neutral and switch live to fire the boiler, and make sure the control circuit is definitely 230v!
If you have a tester and know how to use it then I would proceed but with caution. If you don't then walk away now and call a pro before it potentially costs you an boiler PCB!
 
Can someone please tell me why there new thermostat isn't powering up? I copied the wiring from the old one, with the exception of the earth wire, which I have capped in a wago. Thank you.
The swap is not just as simple as copying the existing wiring, the existing wiring looks like it is just a live and switched live and your new stat would need a neutral, copying the wiring it looks like you might have the live in the neutral connection
The live would also need a link to the switch contact
There are four cables in coming through the wall on the thermostat end, how much help is that? How can I test?
What test equipment do you have
Unless you are familiar with heating control wiring you may be better getting someone in
If you post your location there may be someone on here that is close to where you are
 
You need to confirm that you have 230 / 240v across the brown and the black that has the wago fitted to it if it has then the brown should be connected to terminal 4 with a link connected to terminal 2, the black connects to terminal 3
 
Yes, a multimeter can test for voltage on the right scale setting.

Wrong scale setting will

A word of caution however, that the spare wire may indeed be a neutral, or it may not be connected to anything at the other end.
Testing between your live and this mystery wire may give the impression the circuit is dead when it is not.

The other end of the cable may be in a wiring centre (joint box) rather than straight back to the boiler.
 
Yes, a multimeter can test for voltage on the right scale setting.

Wrong scale setting will

A word of caution however, that the spare wire may indeed be a neutral, or it may not be connected to anything at the other end.
Testing between your live and this mystery wire may give the impression the circuit is dead when it is not.

The other end of the cable may be in a wiring centre (joint box) rather than straight back to the boiler.
Thank you. I was thinking of unscrewing the fused switch from the wall behind the boiler to see what wires are in there. Will all the wires be there or will some go straight to the fuse box?

Any recommended setting?
 
Thank you. I was thinking of unscrewing the fused switch from the wall behind the boiler to see what wires are in there. Will all the wires be there or will some go straight to the fuse box?

Any recommended setting?
It would be unlikely to go to the switched spur, the thermostat could go to the heating controller, the wiring centre or direct to the boiler depends on what type of system you have
 
To consolidate some of the above:
  • Terminal numbers on heating components are not standardised and there is no guarantee of correspondence or compatibility between one product and another. The schematic diagram and technical specs must be checked before use.
  • The original stat behaves like a switch. It does not require power to operate itself.
  • The smart stat also behaves like a switch but requires a continuous supply of 230V AC power for its electronics.
  • If the heating control circuit being switched operates at 230V then the existing cable with three cores plus earth may be adequate for the new stat.
  • The connections at the system wiring centre / boiler might need to be changed, so that the line feed is always live (rather than only being live when demanded by the programmer.) Whether this is possible will depend on the programmer and its wiring. The black core (at present unused) might need to be connected to neutral if it isn't already.
  • If the heating control circuit being switched operates at extra-low voltage, then the existing cable is not sufficient as there would be a need for two power cores and two control cores in addition to the earth.

Most of the information needed can be gleaned from studying the connections in the wiring centre or at least the other end of the stat cable which you need to find. Be prepared for it to be a spaghetti junction.
 

Reply to Wiring a new smart thermostat in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Ignore the post in #3 it is of no help. Hopefully someone may know but it maybe a longshot, have you asked on a more specific appliances forum?
Replies
2
Views
386
  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
857

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top