saint elmo

Trainee
Joined
Aug 4, 2021
Messages
18
Reaction score
1
Location
UK
just thought i would share this i posted about in a previous thread.

1st and 2nd pic- red and white wires going into landing light (connected to downstairs circuit)

3rd and 4th pic- red wire going down, white wire going into the junction box for the upstairs lighting circuit connecting to neutral

5th pic-red wire coming down into upstairs 2 way landing light switch
 

Attachments

  • [ElectriciansForums.net] borrowed neutral (follow up)
    20210806_195539.jpg
    362.3 KB · Views: 58
  • [ElectriciansForums.net] borrowed neutral (follow up)
    20210808_111215.jpg
    386.3 KB · Views: 44
  • [ElectriciansForums.net] borrowed neutral (follow up)
    20210806_195516.jpg
    331.2 KB · Views: 55
  • [ElectriciansForums.net] borrowed neutral (follow up)
    20210808_113529.jpg
    264.3 KB · Views: 46
  • [ElectriciansForums.net] borrowed neutral (follow up)
    20210808_111528.jpg
    312.7 KB · Views: 56
I agree that it appears from the photos the Switched Live is coming from the downstairs circuit and the Neutral for the Landing light is coming from the upstairs circuit.
The thing is, there are so many issues in the photo's that I wouldn't advise tackling this.
It looks to my sleepy eyes as though the red and white are single insulated? Big safety issue....
I think I can see 2.5 and 1.5 T+E cables in the same junction boxes, suggesting maybe lighting and sockets are intertwined too.
No Earth sleeving anywhere.
Awful CPC termination.
Missing sleeving on strappers.
Basically a right mess!

What needs to happen in my view is the upstairs lighting circuit needs a rewire, the white and red wires need taking safely out of service (including at the switch downstairs). The Landing light needs to move entirely to the upstairs circuit.
Then either a new 3 core switch wire or Quinetics switches.
Even though you clearly have knowledge and understanding I would still say this is one for a sparks as it's really quite a mess.
 
I agree that it appears from the photos the Switched Live is coming from the downstairs circuit and the Neutral for the Landing light is coming from the upstairs circuit.
The thing is, there are so many issues in the photo's that I wouldn't advise tackling this.
It looks to my sleepy eyes as though the red and white are single insulated? Big safety issue....
I think I can see 2.5 and 1.5 T+E cables in the same junction boxes, suggesting maybe lighting and sockets are intertwined too.
No Earth sleeving anywhere.
Awful CPC termination.
Missing sleeving on strappers.
Basically a right mess!

What needs to happen in my view is the upstairs lighting circuit needs a rewire, the white and red wires need taking safely out of service (including at the switch downstairs). The Landing light needs to move entirely to the upstairs circuit.
Then either a new 3 core switch wire or Quinetics switches.
Even though you clearly have knowledge and understanding I would still say this is one for a sparks as it's really quite a mess.
yes those red and white wires are single insulated
2.5 and 1.5 T+E cables- yeah thats all lighting and switch cable no rhyme or reason to the size used
all cable has been accounted for and is easier than it looks
they have used 2+E instead of 3+E to connect downstairs switch to upstairs switch hence the need to tap into the upstairs neutral
 
It's not necessarily about understanding where the wires come from, that installation breaks so many regulations and exhibits many very bad practices, such that it doesn't need a bit of a fix here and there, what it needs is completely sorting; running cables and rewiring etc in line with the regulations.

I assume that the rest of the property is similarly bad, so perhaps you need to get someone in to check it out properly.

It isn't just about getting the wires to the right place, it's about making sure it is safe in all aspects.
 

Reply to borrowed neutral (follow up) in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
417

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top