Stupid question probably but... If someone was to bell out a circuit to find a fault, should they disconnect from the board and why? Also, if a light on a two way and intermediate stays o. Perminately would that be due to the strappers being mixed up?

Thanks people

Regards
 
To bell out, is the old way of testing for continuity, and it was a simple doorbell circuit.

nowadays, a multi function tester can send anything up to 1000v down the wire, so not only does the circuit need disconnected from mains, but any electronics or other devices need disconnected from the circuit. Ie, smoke alarms, led lights, anything that can be unplugged!

the question of two way lighting… it is unclear if you mean always off, or always on… maybe edit the post?

if always on, then the supply feed is connected to the switchwire and the switches aren’t doing anything.
mixing up the strappers would cause the light to work on one switch but not the other. Ie a strapper is connected to either the feed or the switchwire.
 
To bell out, is the old way of testing for continuity, and it was a simple doorbell circuit.

nowadays, a multi function tester can send anything up to 1000v down the wire, so not only does the circuit need disconnected from mains, but any electronics or other devices need disconnected from the circuit. Ie, smoke alarms, led lights, anything that can be unplugged!

the question of two way lighting… it is unclear if you mean always off, or always on… maybe edit the post?

if always on, then the supply feed is connected to the switchwire and the switches aren’t doing anything.
mixing up the strappers would cause the light to work on one switch but not the other. Ie a strapper is connected to either the feed or the switchwire.
Thanks for the reply
Got it sorted... Testing between neutral and live with a lamp in.
 
Still widely used in India!

I showed the guy my modern version he turned his nose up at it
 

Attachments

  • [ElectriciansForums.net] Belling out
    20170620_081949.jpg
    203.6 KB · Views: 54
advances in technology.cvwe now have these wonderful machines. batteries not required, and the magic needle eliminates the need for buzzer:

View attachment 88887
Didn't we all start off with one of these??

Still have mine!

Nothing wrong with the term belling out, for simple end to end identification of cores/connections I frequently use the fluke multimeter on diode setting - it buzzes when connectivity is made.
 
I have a Martindale voltage tester that also bleeps on continuity.

Good point is it also warns you of a live circuit without blowing up (different bleep)

Bad point is you jump with proving dead as it bleeps until you remember it is the 'safe' bleep sound...
 
I have a Martindale voltage tester that also bleeps on continuity.

Good point is it also warns you of a live circuit without blowing up (different bleep)

Bad point is you jump with proving dead as it bleeps until you remember it is the 'safe' bleep sound...
My megger one does the same, and yes I jump in panic exactly the same!
 

Reply to Belling out in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
442
davesparks
D
  • Question
We just left it as it was, again the customer didn't seem too bothered, dont think she wanted me digging any further.
Replies
14
Views
1K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
820
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
357

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks