You have not got quite the same faults as what was probably the most annoying problematic job i have ever had since becoming a sparks but this may help ?
It was a boderous boiler (complete and utter useless unhelpful ----ers on their technical side !) run with Honeywell 2 and 3 ports along with a Drayton 2 channel controller .
The problem on this one was every so often the heating would just run on , no matter what you did at the controller and stat .
From memory it it would happen if both heating and hot water were selected and if the hot water became satisfied before the heating then the heating would never stop no matter what you did to it .
I honestly stripped the complete control circuit and re connected it from scratch over 12 twelve time on 8 different visits , it was made worse by the fact it had all come about because they had just had thermal solar installed with the new boiler a controller and valves so this made me question what we had done , so many times ( along with the inept moron at boderous ) !
I eventually called honeywell technical , who instantly said that it was a bit of a design fault on only certain boilers that will allow them to fire up on stray voltage and not just the 230v switch live that you would expect they needed to do it , the remedy was to put a little ( i think ) capacitor between Live feed in and sw live out on the zone valve as they never truly shut down and can allow around 30v through even when idle , if configured in a certain order !
The Honeywell technical chap even sent several photo copy's of the wiring diagram on how to do it and a handful of capacitor's for free !!!
Maybe worth a phone call to them if you have honeywell valves ?!
It was a boderous boiler (complete and utter useless unhelpful ----ers on their technical side !) run with Honeywell 2 and 3 ports along with a Drayton 2 channel controller .
The problem on this one was every so often the heating would just run on , no matter what you did at the controller and stat .
From memory it it would happen if both heating and hot water were selected and if the hot water became satisfied before the heating then the heating would never stop no matter what you did to it .
I honestly stripped the complete control circuit and re connected it from scratch over 12 twelve time on 8 different visits , it was made worse by the fact it had all come about because they had just had thermal solar installed with the new boiler a controller and valves so this made me question what we had done , so many times ( along with the inept moron at boderous ) !
I eventually called honeywell technical , who instantly said that it was a bit of a design fault on only certain boilers that will allow them to fire up on stray voltage and not just the 230v switch live that you would expect they needed to do it , the remedy was to put a little ( i think ) capacitor between Live feed in and sw live out on the zone valve as they never truly shut down and can allow around 30v through even when idle , if configured in a certain order !
The Honeywell technical chap even sent several photo copy's of the wiring diagram on how to do it and a handful of capacitor's for free !!!
Maybe worth a phone call to them if you have honeywell valves ?!