Hi, I’m a bit new to this and I understand how to wire thru a grid key switch for emergency lighting but could someone please explain or show a small drawing how to wire with a key switch so when the key switch is toggled, the lights stay in and only turns off the emergency lights please
 
Just break the permanent or emergency feed through the key switch. The switch feed to the rest of the lights should be totally separate.
Anyone ever seen this done properly.. emg lights only controlled by key switch & not looped of in circuit with other ordinary lights
 
The way I seen them done is CTU and multipole n/c contactor in the DB

Each lighting MCB you take a feed through a pole for emergencies

Ctu breaks the poles
 
Interesting...
I am no expert on this, but in a recent installation of maintained units, a separate permanent live was installed, without key-switches. Thus, when doing monthly testing we just trip the breaker for the lights and check that the ones with emergency modules stay lit...which they do. We don't check for them staying on for 3 hours, but an hour is fine, as the building is small and can be evacuated in under 2 minutes via 3 exits. Probably not "best practice" but for a small building it works fine.
 
Interesting...
I am no expert on this, but in a recent installation of maintained units, a separate permanent live was installed, without key-switches. Thus, when doing monthly testing we just trip the breaker for the lights and check that the ones with emergency modules stay lit...which they do. We don't check for them staying on for 3 hours, but an hour is fine, as the building is small and can be evacuated in under 2 minutes via 3 exits. Probably not "best practice" but for a small building it works fine.
I don't get that?
 
Yes, that's pretty much it. Basically, a P/L which keeps the battery charged. However, should the RCBO trip, the emergency option is triggered, and the luminaire stays lit, on battery power. They have an LED on the frame which shows green when all is well and the battery is charging, and red when in emergency mode. Thus, when the luminaire is switched off, at the switch, the battery is still being kept on charge. Tripping the RCBO simulates a loss of power. That is how it is tested, instead of having a key switch in the circuit.
 
The top drawing is preferred as the test facility only isolates the permanent supply, the bottom drawing will also isolate the general lighting.
 
The top drawing is preferred as the test facility only isolates the permanent supply, the bottom drawing will also isolate the general lighting.

Is it the same lamp powered by the switched live as the battery

You turn off the switched live ,the lamp goes out and then the key switch brings it back on to prove the backup system ?
 
Last edited:
Led maintained bulkhead

What 50,000 hrs life ,low.wattage

Is there any need to be messing with switched lives ?

Keyswitch or rcbo as above and leave it on 24/7 I dunno ?
 
Is it the same lamp powered by the switched live as the battery

You turn off the switched live ,the lamp goes out and then the key switch brings it back on to prove the backup system ?
A maintained emergency light can act in the same way as a normal general light the only difference being the separate permanent supply controlled by the test facility. Aside from that it will switch on and off like any normal light. A maintained fitting will generally have four terminals L1, L2, N and earth although manufacturers may identify the terminals different for L1 and L2.
 
A maintained emergency light can act in the same way as a normal general light the only difference being the separate permanent supply controlled by the test facility. Aside from that it will switch on and off like any normal light. A maintained fitting will generally have four terminals L1, L2, N and earth although manufacturers may identify the terminals different for L1 and L2.
Ya I'm familiar with that

What about the led why bother with on/off
 
Can happen sometimes in an emergency that the general lighting isn't on

Makes sense then to leave the led permanently maintained
 
Why bother using it as a general light with backup

With LEDs characteristics long life and low power

I would have thought just keyswitch to L1+L2 and permanently maintained
This type of light would of the same type as the general lighting for aesthetics not the bulkhead style you may be thinking off therefore it operates in the same way as all the other fittings.
 

Reply to Key switch for emergency lights in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Fitted a lot of this sort of light recently, with all tests reporting back through central Dali controller(s).
Replies
15
Views
687
nicebutdim
N
If it's going to be an emergency stop and not just a stop, then other factors come into play depending on what sort of machines the emergency stop...
Replies
11
Views
784
G
I've seen this a few times where the wire from the alternator has been connected to the wrong terminal on the starter motor solenoid. In a...
Replies
2
Views
437
It could be a slave switch where you would have a L in and a common wire out to a master switch.
Replies
3
Views
522
As if my handle doesn’t give the biggest hint. The pod light above the winch is the one I’m referring to. I don’t foresee any issues with using a...
Replies
2
Views
231

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks