What’s the connections on the new thermostat?
It's the GC variant.
Wired like this the boiler is always on regardless of stat temp setting. As I cycle the temp up and down I can hear the relay operating. Is there a bench test to ensure stat is working properly?Brown to 4
Grey/blue sleeve 3
Black/brown sleeve 2
Link cable from 4 to 1
Why would the output from the relay (diagram top left) o/p 1 and 2 (n/o and n/c) link to the Neutral?
Sorry, got it, it isn't a n/o - n/c output, it's showing an actuator.... is it?
So I wired 4 and 3 to the mains and bridged 4 to 1. A meter across 2 and 3 shows 240 regardless of stat setting. I'm no genius, but this to me would indicate a busted stat?Brown to 4
Grey/blue sleeve 3
Black/brown sleeve 2
Link cable from 4 to 1
So I wired 4 and 3 to the mains and bridged 4 to 1. A meter across 2 and 3 shows 240 regardless of stat setting. I'm no genius, but this to me would indicate a busted stat?From the way the original t6360 was wired, the black wire with brown sleeve ought to be switched live to the boiler.
You could try disconnecting that one (isolating/insulating it) from your new thermostat, and checking the boiler doesn't run. If it does, there's some other wiring issue in play, or something else is calling for heat!
The relay has now stopped clicking and the heating on indicator remains off regardless - although 240 is present across 2 and 3. This stat is from Wish.com and has functioned faultlessly for several years. It has rattled around in my tool box for the last 12 months - perhaps taking fatal damage along the way. When powered down - continuity across 1 and 2.If it's a brand new stat It's unusual to be immediately duff!
I suppose the relay contacts could have welded together by some accident, but you can hear it clicking?
if you've got a multimeter, with the stat totally unpowered/disconnected, are 1 and 2 connected together (zero ohms)?
if so - busted!