just wondering if anyone can recommend an MFT that doesn't suffer (much) from RCD uplift? my megger 1710 is definitely not on the list :angry:
 
In the article above, it gives an example of an RCD adding an impedence of 0.5ohms to the circuit. Surely then that is part of the total loop impedance and should be included in the result, rather than being identified and subtracted? Or does it only appear to add that impedance to the test current, and behaves differently when a fault current is applied?
 
In the article above, it gives an example of an RCD adding an impedence of 0.5ohms to the circuit. Surely then that is part of the total loop impedance and should be included in the result, rather than being identified and subtracted? Or does it only appear to add that impedance to the test current, and behaves differently when a fault current is applied?
Dunno shaun
 
What in Heaven is an RCD uplift??????????

It's just a word to describe the odd way that some RCDs can appear to increase the earth fault loop impedance of a circuit, usually as a result of the way an anti trip test is carried out.

In my experience the problem varies between RCD manufacturers as well as between different test meters.
 
In the article above, it gives an example of an RCD adding an impedence of 0.5ohms to the circuit. Surely then that is part of the total loop impedance and should be included in the result, rather than being identified and subtracted? Or does it only appear to add that impedance to the test current, and behaves differently when a fault current is applied?

Quite often it only appears to add impedance to anti trip type tests.
 
At last an end to troublesome uplift!!
Hallelujah!
What could the answer be, oh yes the author of the thread happens to also sell the solution :)

I think rather than pay for a new tester, I might just carry out a loop test on both sides of the RCD

Megger are basically implying that their previous MFTs with lo current loop testing are not up to scratch then surely......???!!! Maybe I will ask for a part refund on the cost of my Megger due to them selling me an item that is slightly 'duff'.....
:confused:
 
Megger are basically implying that their previous MFTs with lo current loop testing are not up to scratch then surely......???!!! Maybe I will ask for a part refund on the cost of my Megger due to them selling me an item that is slightly 'duff'.....
:confused:

And they have known about this problem for years but didn’t bother mentioning it till now.
Not all RCDs just some and not all of the time, so they must have details of the ones that cause problems? That information would be very useful
 
Being on the sick list and bored, I did a little science experiment, using a desktop TNCS, a new Wylex B32 DP RCBO (with Type A RCD characteristic) and my KT65 MFT.
The average results I got were less than 0.02 Ohms uplift through the device. This surprised me in that I’ve seen 0.1 - 0.2 on a couple of real circuits that I’d done the alternate method hi current test. The DC continuity test gave 0.00 Ohms across the device. As I’d expected, the new RCBO passed the 6 RCD tests and had 24mA trip on ramp test.
So I’m thinking - either some RCDs are more prone to this problem than others - or - my test was rubbish.
 
think i've posted this before, ages ago. went to a call where BG had refused to connect boiler. Zs was well over 100 according to his socket tester. checked with MFT and got 352 ohms. thought maybe a useless rod, but when I checked the supply , it was TNC-S. Ze measured at 0.2 ohms. when I tried reading on the load side of the upfront RCD I got 349 ohms. that's more uplift than Katie Price. It was one of the old type RCCBs, lever switch on front, forget make now. may have been MEM,
 
Last edited:
In the article above, it gives an example of an RCD adding an impedence of 0.5ohms to the circuit. Surely then that is part of the total loop impedance and should be included in the result, rather than being identified and subtracted? Or does it only appear to add that impedance to the test current, and behaves differently when a fault current is applied?

apparently the extra impedance is only due to the way the loop impedance measurement is made and it is not normally "seen". otherwise there would be a lot of very warm RCDs about! In another article I saw its referred to as "ghost resistance"
 
I think rather than pay for a new tester, I might just carry out a loop test on both sides of the RCD

Definitely. but i think that a lot of electricians don't even know this issue exists. maybe it should be recommended as good practice to measure at both sides of the rcd to check for uplift and then subtract as necessary.
 
Adding to this post from my recent experience with Contactum Defender boards. In the split board I have on this installation the two 80A 30mA rcds are adding 0.8 Ohms to the Zs. Same on both, so reasonable to presume it's not a rogue unit. This puts all the ring circuits well above the Max Zs for 32A B mcbs. I'm surprised not to find more discussion about this around the various forums.... or do I acutually have two identically dodgy RCD units in this board? .... come to think of it as they came loaded in the board it could be a particularly dodgy batch ??
 
posted on another thread, this solves it at no cost with any MFT.
[ElectriciansForums.net] Best MFT to avoid RCD uplift?
 
There is an ongoing argument at the moment about manufacturers both those who make rcds/rcbos and mfts as they all have there own interpretation of the standards and regs...
The ECA came out with a cracker recently when they said we only need to record the type ac trip times on the schedule of test results and not type a, b etc...
Likewise lewden said their rcbos work with the standard but mfts cant test them!
Megger just pleased ignorance and came back with something about the mft having a wide range ...
Seems everybody is doing their own thing. Not sharing info due to proprietary tech etc and everybody is confused
 
my megger 1721 will test all types. just a setting to set for each. even my old (2008) 1553 can be set for AC or A types.
 

Reply to Best MFT to avoid RCD uplift? in the Electrical Tools and Products area at ElectriciansForums.net

Similar Threads

How I wish I’d read this 6 weeks ago before I bought the thing. All you say is true and my strap did give way sending the tester plummeting to the...
    • Informative
    • Like
Replies
19
Views
7K
Good point !
Replies
14
Views
4K
Ok I’ll try this when I’m down
Replies
4
Views
276
If the main DB RCBO is there to provide additional protection (as it most probably is), then no, as S type RCDs are not suitable for providing...
Replies
1
Views
1K
loz2754
L
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Replies
21
Views
1K

Electricians Tools | Electrical Tools and Products

Thanks for visiting ElectriciansForums.net, we hope you find the Electricians Tools you're looking for. It's free to sign up to and post a question yourself to find a tool or tool supplier either local to you, or online. Our community of electricians and electrical engineers will do their best to find the best tool supplier for you.

We also have a Tiling Tools advice from the worlds largest Tiling community. And then the Plumbers Forums with Plumbers Tools Advice.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Trending Electricians Tools

New job, new tester; Megger 1741+, those that have one; anything good/bad to report? Work also trusting me with a Flir E5 magical heat-reading...
Replies
210
Views
95K
Absolutely correct they hold water, shrouds are totally unnecessary. 20s is 24mm spanner, 20 large is 30mm spanner.
2
Replies
41
Views
45K
If that little thing, plugs your butt, you better eat slowly. 🤣
    • Like
2 3 4 5 6 7 8 9 10 11 12 13 14
Replies
336
Views
41K
B
I'd say everyone has knowledge gaps in their area of electrical work I know i have quite a few i work on to fill them in
2 3 4
Replies
75
Views
29K
I too have been tempted.. I’m buying for my son. He’s in his2nd year at collage and looking for apprentiship. Sadly it’s almost impossible in my...
Replies
11
Views
25K
Of course. “Ye canna change the laws of physics” EDIT. oh blimey, I just spotted the date of the OP. ? Thank you very much @Lord lee jan You...
Replies
40
Views
23K
Only way to do it in a tight space
2
Replies
33
Views
21K
The display on the Mft pro is not very durable mine is broken already 😡
2
Replies
29
Views
21K
Only lawyers , solicitors and dodgy chat up lines charge for picking up the telephone 🙃
2 3 4
Replies
97
Views
20K
J
I'm not entirely certain as it's very tough, but brittle when cold.
2 3
Replies
65
Views
19K
nicebutdim
N

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks