Hi Everyone,
I'm New to this forum and am hoping to obtain some advise if possible please?
I have a situation where a megaflow system is installed in the Attic of a semi detached property.
The Immersion heater switch has been installed by someone in the airing cupboard which sites at the end of the bath tub ( and has been disconnected from the Consumer Unit).
It has been wired with 2.5 T&E up to the isolation switch and then from the switch it is connected via flex cable to the Immersion heater.
This means that the Switch is inside Zone 1 as the bathroom does not extend to 3 meters in length where the switch can be installed.
Where Can I re-allocate the Switch for the Immersion heater?
Can it be installed on the outside of the bathroom above the door besides the extractor fan Isolator switch?
Will I also need to re-route the cabling for the Immersion heater as it is in plastic conduit passing Zone 1 as attached on the picture?
The upstairs lighting is also routed via plastic conduit - will I need to remove all the wiring from this location and reroute it from outside Zone 2 or the bathroom altogether?
Thanks,
K
I'm New to this forum and am hoping to obtain some advise if possible please?
I have a situation where a megaflow system is installed in the Attic of a semi detached property.
The Immersion heater switch has been installed by someone in the airing cupboard which sites at the end of the bath tub ( and has been disconnected from the Consumer Unit).
It has been wired with 2.5 T&E up to the isolation switch and then from the switch it is connected via flex cable to the Immersion heater.
This means that the Switch is inside Zone 1 as the bathroom does not extend to 3 meters in length where the switch can be installed.
Where Can I re-allocate the Switch for the Immersion heater?
Can it be installed on the outside of the bathroom above the door besides the extractor fan Isolator switch?
Will I also need to re-route the cabling for the Immersion heater as it is in plastic conduit passing Zone 1 as attached on the picture?
The upstairs lighting is also routed via plastic conduit - will I need to remove all the wiring from this location and reroute it from outside Zone 2 or the bathroom altogether?
Thanks,
K