Line carrying voltage, neutral no voltage | on ElectriciansForums
Discuss Line carrying voltage, neutral no voltage in the UK Electrical Forum area at ElectriciansForums.net
Cheshire
Hi all, I have been trying to work out why all the up stair sockets have voltage coming into the line but none of the neutrals.
The ring is on a 16amp mcb. Any ideas why?
Thank you in advance
That would seem a normal scenario, but not sure I understand. Exactly what are you measuring and what is the issue?
just ignore me - everyone has asked the same thing - give some clarity Anthony ?
Apologies. the the RCD shares the up and down sockets. When I test the sockets on the Kewtech on the trip Le rcd, insulation etc it shows no voltage. I press test and the RCD trips. GGGrrrrrrrrrrr
[ElectriciansForums.net] Line carrying voltage, neutral no voltage
I'm not au fait with mfts prefer separates so I can only assume it is indicating a poor earth path. The fault loop path is line to earth which the meter is looking for so if the earth is not there it may indicate 0v.
I think DPG meant measuring the voltage directly.
By the way I think you have the L and N leads plugged in the wrong way round on the back of the Kewtech, unless I'm reading the wrong manual ?
I have a similar Kewtech though mine isn't a 'plus'.
You are right, you should see the Line/Neutral voltage on the screen at that point.
From the manual:
So you are right to raise your eyebrows.
I've just noticed you said ALL upstairs sockets are like this. Are they on their own circuit or same ring as downstairs?
Have you re-proved the tester and test leads are working downstairs or elsewhere since discovering this?
I'd put the MFT down and pick up the 2 pole tester and go back to first principles, L-E and L-N tests at all sockets, maybe check wiring for circuit at CU too. Until you are seeing a normal supply at the sockets there's no point proceeding with loop tests. Logic will eventually prevail...
This is an interesting one, so do report back!
From the manual:
Hi, upstairs sockets are on a different breaker yet share the same RCD. All leads Nulled and yes will try again tomorrow and do and EICR on the fuseboard.
Thank you
Reply to Line carrying voltage, neutral no voltage in the UK Electrical Forum area at ElectriciansForums.net
View: https://www.youtube.com/watch?v=glsg2HpWyok
Hi Mike, Floating Neutral. I'm really over simplifying below, but using generators as an analogy is possibly easier to understand. In a large 3...
Not all sockets isolate both the live and neutral when you turn the switch off Many just isolate the live leaving the N connected. So the...
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3
4K
And exciting when that Hager AFDD finally tripped 😂
nicebutdim
N