BS951 clamp used for TNS? | on ElectriciansForums

Discuss BS951 clamp used for TNS? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,278
Reaction score
5,773
Location
Gloucestershire
I have just completed an EICR.

The earthing is TN-S. However, there is a BS951 clamp used for this. Is this acceptable? Did the DNO ever use this a BS951 as a means for clamping around the supply cable or would this always be DIY?

Ze is 0.23ohms, but that doesn't mean a great deal if the connection is not compliant.

Picture below, albeit a little poor. Ignore the bottom clamp, this is to gas. It is the clamp partially obscured by the meter tails.

[ElectriciansForums.net] BS951 clamp used for TNS?
 
Some did even though they aren't supposed to. Should be either a sweated connection or constant force spring (similar to that used on SWA joints), I'd C2 and a call to 105.

133.1.3 - clamp not appropriate for use.
Thanks Lister.
 
If you do a lot of domestic work you will see loads and loads of pipe bonding clamps used to make a tns connection on the lead sheath

so common in fact that if the clamp looks in good condition and i get a decent Ze , then i don't even bother noting it anymore
 
I don't like it at all, personally. Although usually they will give a satisfactory resistance reading, there might only be small points of contact due to the low clamping force, I wouldn't trust it under fault current. If for any reason it penetrates the lead, it can start a fireball that stops only when the substation or feeder pillar fuse blows. Most unlikely, but avoidable, hence I would note it.
 
That clamp is newish and the same make/age as the main gas bond clamp. So I'm assuming someone felt the need to 'upgrade' during a board change, the original earth was most likely bare etc.
Too many people misguidedly mess with the DNO cable sheath in this way, as Lucien points out there could be a massive fuse behind it - a single service cable can be jointed off a really big cable quite legitimately in line with supply regs so could well be an 800amp fuse or higher ! So in technical terms - bugger that ! ?
 

Reply to BS951 clamp used for TNS? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
It’s on the lead.
    • Like
Replies
9
Views
5K
E
Welcome @Geraldine you may be better off starting a new thread with more detail as Edd is no longer a forum member.
Replies
60
Views
80K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks