Hi All,

I have a FCU rated at 1.1 kW (3 speeds) but stating 2.8 A (FLA).

Can anyone explain me what FLA is and why 3.8 A? If I make my maths: 1100 W / 230 V is 4 78 A.

Not sure what I am doing wrong. Thank you.
Mark
 
Can you tell us what you mean by FCU, over here (UK) if often means Fused connection unit.

1.1kW and 2.8A works for 400V but it would be unusual for a single phase load to be connected phase-phase.
 
If you look at motor current charts the FLA does state its 2.8A for a 1.1kW motor at 380Vac.

[ElectriciansForums.net] Meaning of Full Load Amperes (FLA)
 
FCU: Fan Coil Unit.

But also.... apologies... I will try to modify my thread as it's a 3phase fancoil.

Yet...

1100 / (400 * sqrt 3) should be 1.58 A. Not 2.8 A.
Not sure what I'm calculating wrong.
Thank you

There is also the Power Factor and Efficiency of the motor that has to be taken into account.
 
Correct... even if I wanted to consider 0.8 for both PF and efficiency... I dont get anything grrater than 2.5A.... ?

Is there no plate on the motor telling you the Efficiency and Power Factor?
 
I think my confusion comes from the fact I don't know the definition of FLA or FLC.

Also, have a look at this picture.
I cannot figure out the maths to confirm the current given once I have voltage, power, power factor and efficiency
 

Attachments

  • [ElectriciansForums.net] Meaning of Full Load Amperes (FLA)
    IMG-20211228-WA0010.jpg
    38 KB · Views: 35
I note that the motor is 1.5kw
the fan is 1.16kw

it is normal for the motor to be slightly higher rated than the fan as it prevents the motor from being run in a slightly overloaded state and therefore overheating.

the motor itself will have a nameplate that shows the full load current.
 
I note that the motor is 1.5kw
the fan is 1.16kw

it is normal for the motor to be slightly higher rated than the fan as it prevents the motor from being run in a slightly overloaded state and therefore overheating.

the motor itself will have a nameplate that shows the full load current.
For some reason I thought that a fancoil only had 1 motor: the fan. But ot seems that this plate differentiates between motor AND fun. Not sure to understand the difference. But if I put some numbers is.... 1.5 kW; 400V; 0.83 eff; maybe a 0.8 PF... we will get more or less the 3.42 A stated.
Also, I can see that my Single Line Diagram only reported the rating of the fan (1.1 kW) but the FLA of the motor it seems.

Question is... if not the fan, what's the motor doing in a Fancoil?
 
The motor converts electrical energy to a rotating force (speed x torque=power)
the fan converts the rotation to a forward flow of air or other fluid.

what are you trying to figure out?
wiring, suitable motor overload etc?
 
There is only one motor, the fan motor.
By 'Motor kW' it means the maximum rated mechanical output power of the motor, as decided by the motor manufacturer.
By 'Fan absorbed power' it means how much mechanical power the impeller absorbs from the motor shaft, as decided by the FCU manufacturer.

So the motor is capable of 1.5kW but the impeller only applies 1.16kW of load to it, leaving a margin so that the motor is not worked to its maximum. However, the full load current is specified for the motor working at 1.5kW mechanical output (P2) and it is a reasonable figure given the rated 415V supply voltage and 83% efficiency (I've taken the power factor as 0.75):
1500 / 0.83 / 0.75 / 415 / sqrt(3) = 3.35A
Which compares well to the stated 3.42A.

With the fan impeller taking only 1.16kW instead of 1.5kW the actual line current will be lower, although not by the factor 1.16/1.5 because only the in-phase current will be reduced, not the magnetising current (and the pf will be lower).
 

Reply to Meaning of Full Load Amperes (FLA) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thanks, this is super helpful and makes sense.
Replies
4
Views
1K
  • Question
Thanks indeed, Lucien, RE THE ABOVE If each coil has one of the three phase connected to it, and a delta configuration has only three supply...
2
Replies
25
Views
7K
Background I live in Indonesia, the voltage for residential buildings ranges from 220 V to 230 V, I need help with the installation of the...
Replies
0
Views
3K
  • Question
Post in thread 'Domestic - Voltage fluctuations on a 1000VA 600W UPS with 40% load when on battery' by kuddoo has been reported by kuddoo. Reason...
Replies
0
Views
94
I hear many views of people who believe that DPF's and CDPF's fitted to their vehicles are a problem and many people resort to removing them, or...
Replies
0
Views
8K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks