Hi All,

I have a FCU rated at 1.1 kW (3 speeds) but stating 2.8 A (FLA).

Can anyone explain me what FLA is and why 3.8 A? If I make my maths: 1100 W / 230 V is 4 78 A.

Not sure what I am doing wrong. Thank you.
Mark
 
Can you tell us what you mean by FCU, over here (UK) if often means Fused connection unit.

1.1kW and 2.8A works for 400V but it would be unusual for a single phase load to be connected phase-phase.
 
If you look at motor current charts the FLA does state its 2.8A for a 1.1kW motor at 380Vac.

[ElectriciansForums.net] Meaning of Full Load Amperes (FLA)
 
FCU: Fan Coil Unit.

But also.... apologies... I will try to modify my thread as it's a 3phase fancoil.

Yet...

1100 / (400 * sqrt 3) should be 1.58 A. Not 2.8 A.
Not sure what I'm calculating wrong.
Thank you

There is also the Power Factor and Efficiency of the motor that has to be taken into account.
 
Correct... even if I wanted to consider 0.8 for both PF and efficiency... I dont get anything grrater than 2.5A.... ?

Is there no plate on the motor telling you the Efficiency and Power Factor?
 
I think my confusion comes from the fact I don't know the definition of FLA or FLC.

Also, have a look at this picture.
I cannot figure out the maths to confirm the current given once I have voltage, power, power factor and efficiency
 

Attachments

  • [ElectriciansForums.net] Meaning of Full Load Amperes (FLA)
    IMG-20211228-WA0010.jpg
    38 KB · Views: 40
I note that the motor is 1.5kw
the fan is 1.16kw

it is normal for the motor to be slightly higher rated than the fan as it prevents the motor from being run in a slightly overloaded state and therefore overheating.

the motor itself will have a nameplate that shows the full load current.
 
I note that the motor is 1.5kw
the fan is 1.16kw

it is normal for the motor to be slightly higher rated than the fan as it prevents the motor from being run in a slightly overloaded state and therefore overheating.

the motor itself will have a nameplate that shows the full load current.
For some reason I thought that a fancoil only had 1 motor: the fan. But ot seems that this plate differentiates between motor AND fun. Not sure to understand the difference. But if I put some numbers is.... 1.5 kW; 400V; 0.83 eff; maybe a 0.8 PF... we will get more or less the 3.42 A stated.
Also, I can see that my Single Line Diagram only reported the rating of the fan (1.1 kW) but the FLA of the motor it seems.

Question is... if not the fan, what's the motor doing in a Fancoil?
 
The motor converts electrical energy to a rotating force (speed x torque=power)
the fan converts the rotation to a forward flow of air or other fluid.

what are you trying to figure out?
wiring, suitable motor overload etc?
 

Reply to Meaning of Full Load Amperes (FLA) in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
181
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
556
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
515

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top