Ahh see, this is what I am interested in. What are the BST rules on the length of the unprotected length of secondary cable?
None.
I don't think you quite understand, our rules are not like your rules, (but a bit different,) they follow a quite different philosophy.
You have it spelt out "x length in these circumstances" etc etc.
Our rules are "distribution must disconnect within 5 seconds " etc etc.
Therefore there isn't actually any unprotected cable (although I and others use the term), it really means there isn't "our" protection on the cable.
In the case of a transformer the cable from the secondary to the switchgear bus, and the secondary itself is protected by the primary side protection.
How long therefore - well it must disconnect in 5s in the event of a fault.
So ulike your codes, the length isn't specified, it is determined by the characteristics of the installation.
(Utilities don't necessarily have this rule, although they usually follow the 5s just the same now. They used to have whatever was the limiting time, so if the transformer can withstand a direct short for 15s, but adiabatic calculations on the secondary cable indicate 14s, but then again adiabatic on the primary cable is 10s, then the design limit would be less than 10s)
The only time length is used is where it is actually arbitrary because the installer doesn't have the information.
So for example, a utility will provide a supply to a customer, it will have a fuse (100A, 80A, 60A or rarely 40A) - which size you probably don't know.
The installer then knows that it must go through their own protective device within 3m - could be a simple fuse switch, or could be the actual distribution panel (known as the consumer unit - cu here) with fuses/mcb/rcbo...
This philosophy follows right through our regulations, final circuits don't have a maximum length defined , that comes out of calculations, it must disconnect within x seconds (depends on the type of installation/earthing arrangements), and have less than y voltage drop... etc.
There are guide books that rationalise the above into very conservative guidelines, so on a typical installation, on a 6A type B mcb using 1.5mm^2 cable "z" metres of cable is the maximum length to stay within volt drop and disconnect times etc.
These are not part of the regulations, just shortcuts reducing the need for the calculations.