Hi, I've had an unusual result from taking a Ze at a clients house and wondered what everyones take on it would be:
The property is TN-C-S
A Ze reading from a disconnected Earth to Line gave a reading of 0.45 ohms
A Ze reading from the Line and Neutral gave a reading of 0.33 ohms
A TN-C-S supply should be no more than 0.35 ohms
I'm sure the Ze readings should be the same, but I could be having a senior moment. What concerns me, is that one is out of range, the other is fine. So have I got an issue to refer to the DNO or not ?
Just to add, I might have been a numpty. I disconnected the earth from the earth bar in the consumer unit, but the earth bonding came from a MET to the water and gas, which was still connected, so potential for parallel paths. I suspect I should have disconnected from the MET not the CU. Would that explain the values I've seen ?
The property is TN-C-S
A Ze reading from a disconnected Earth to Line gave a reading of 0.45 ohms
A Ze reading from the Line and Neutral gave a reading of 0.33 ohms
A TN-C-S supply should be no more than 0.35 ohms
I'm sure the Ze readings should be the same, but I could be having a senior moment. What concerns me, is that one is out of range, the other is fine. So have I got an issue to refer to the DNO or not ?
Just to add, I might have been a numpty. I disconnected the earth from the earth bar in the consumer unit, but the earth bonding came from a MET to the water and gas, which was still connected, so potential for parallel paths. I suspect I should have disconnected from the MET not the CU. Would that explain the values I've seen ?