Have ‘pretty big’ new build house we’re wiring from scratch.
New supply in from DNO is PME, but we have Ze of 0.51 😕
Are DNO obliged to keep this under 0.35?
Wouldn’t be that much of an issue normally if regular size house and meter was attached to house.
Before we came along on the scene Client had separate garage block built, meter permanently sited in here.
We’ve run a SWA sub-main across to house DB 25metres away, but struggling on suitable overcurrent protection. Even at 80amps BS 88…. Max EFLI 0.40!
Don’t really want to be putting new build on TT system, if it comes to it.
Thank you
Sy
if disconnection times cannot be achieved by the Breakers then residual current devices can be used.
no need to TT. a PME with a slightly high Ze gives a far better EFLI than any TT could achieve.
although a combination of earth rod and pme may be in order in case of dropped neutrals, but that’s a whole different thread on an abandoned proposed reg change.
Have you spoken to the DNO about it.
They might sort it out.
Did raise my concerns with Client before Xmas.... DNO apparently came out straight away (I wasn't on site) said no problem all fine !
Re-checked last week still 0.51😠
I'm going to raise it myself again directly with them, making sure I'm onsite when (if) they re-visit.
Thanks Pete
How does that work with my 80amp sub-main supply though max EFLI is 0.40 for BS-88 ?
My thinking for TT as an option, was if so could then put all on an RCD (time delayed for sub / house db rcbo's) and use 1667 for max ZS values.
Maybe I'm missing something - has been long week!
Thanks Pete
Yes, time delayed rcd on distribution circuits, standard rcd on final circuits - rcds as fault protection.
No need to convert to TT
leave it as TN-C-S and you can still use 0.4s / 5s but add rcd as fault protection where required.
So if the cable from the meter location to cu fails to operate in 5s due to fault, add a time delayed rcd.
If any final circuit fails to operate in 0.4s due to fault add a standard rcd.
If a circuit will operate within these times, then a rcd is not required for fault protection, but may be required for additional protection.
You also need to consider the protection for L-N faults which won't be covered by adding RCD's. This often gets missed.
If you have a circuit that has cpc size equal or greater than the neutral and you have inadequate fault current to operate ocpd fast enough with regard to thermal constraints, then you will have same issue with L-N faults. You can add RCD to cover the L-E fault protection, but L-N will not be covered.
Yes, you still need overcurrent protection for fault protection, and where necessary overload protection, but there is no requirement to achieve the same trip time.
You also have to achieve voltage drop limits etc, etc - basically all the other requirements remain in place.
Using rcd for fault protection is merely a technique to achieve ads
The disconnection times only need to be met for L-E faults, as far as the regs are concerned anyway. Though interestingly there is something in the OSG that leads you to believe they do need to be met for L-N faults. I'll find a page number...
7.2.4 on p77, note that it doesn't reference any regulation though:
[ElectriciansForums.net] High Ze causing headache !
It's also the thermal constraints part you need to comply with not just disconnection time. I'm not near my big blue book but it is in there. You have to use the 0.1s value of MCB and use it in the adiabatic to confirm.
The disconnection times are to do with protection against electric shock, so I'm not sure why the OSG asks for them to be met for a L-N fault, as no exposed parts would go live.
Unless, perhaps on a TN-C-S, could a significant voltage appear at the MET due to the high voltage drop under such a fault??
Indeed, I think I read your post pre-edit so got the wrong end of the stick
Why would you use 0.1s for this calculation?
And of course all other aspects of the regs still apply, the use of an rcd to achieve one aspect of the regs, doesn't mean other aspects are no longer required.