so after sleeving or taping the twisted earths, put the single cable in 1 light terminal, and the loop with the bit of insulation missing in the other. then if the new fitting is classI (metal with an earth terminal, connect the twisted earths to that).
1. it works..... hooray
2. it doesn't work........ aaaah shyte
3. it goes bang........ call in a sparks.
Surprised to see a post like this from a esteemed professional! As I've posted on here before, we install electrics to fail, not just to work. Anyone, slightly above the level of idiot, can make electrics 'work' - it's what happens when things start to fail that's the difficult bit. To ensure that it disconnects itself in such a way as to present as little danger as possible to life or property.
The twisted earth is very likely to be more than one wire twisted together, so the integrity of the connection is important to maintain earthing to other parts of the circuit. Twisted wires are not sufficient.
1. "It works". Maybe it does, but what's going on behind the panel? More DIY twisted together wires, that may have been loosened by pulling the wires while attaching the new light?
2. Lucky! The fault happened right away, before it could start carbonising, destroying insulation, and potentially cause a fire.
3. The safest outcome.
 
Thank you all for your replies.

The new light fittings are dimmable and the fitting type is E14 (SES). It doesn't come with a place to connect earth and there isn't any reference to earth in the instructions.
with E14 and E27 bases, it'sstandard practice to wire L to the centre contact and N to the outer. however, with the newer fittings, it does not matter so much as the thread is insulated from the supply cables
 
with E14 and E27 bases, it'sstandard practice to wire L to the centre contact and N to the outer. however, with the newer fittings, it does not matter so much as the thread is insulated from the supply cables
I've just found details in the specification confirming that it is double insulated.
 
Ok. I'll explain the concern.
The "partial rewire" would not have included these unless you moved in before 2004 as they are black sheathed. It's also not common way of doing domestic wiring, and hasn't been used that widely since the 70's/80's. I see cables like that in old schools / hospitals a lot, and occasionally in older houses.
All of this makes it look like this wiring hasn't been checked by a sparks, and a decent sparks wouldn't have left the earth wires like that.
Therefore we are concerned for your safety, and suggest you get a bit of help to help advance this project.
Contrary to rumours, most sparks aren't out to scam you, and this would be a quick visit. Many would not even charge for dropping by to help sort out what is going on. Whereabouts are you in the UK?
 
Ok. I'll explain the concern.
The "partial rewire" would not have included these unless you moved in before 2004 as they are black sheathed. It's also not common way of doing domestic wiring, and hasn't been used that widely since the 70's/80's. I see cables like that in old schools / hospitals a lot, and occasionally in older houses.
All of this makes it look like this wiring hasn't been checked by a sparks, and a decent sparks wouldn't have left the earth wires like that.
Therefore we are concerned for your safety, and suggest you get a bit of help to help advance this project.
Contrary to rumours, most sparks aren't out to scam you, and this would be a quick visit. Many would not even charge for dropping by to help sort out what is going on. Whereabouts are you in the UK?
In Worcester

[ElectriciansForums.net] Wiring wall lights, which is live and neutral?
 
Nope, we had a partial rewire done and all existing wiring circuits were checked when we moved in.
Looks extremely dubious. All live conductors the same colour and earth's butchered. No half decent spark would have left anything like that.
 
The fact that something electrical works' does not necessarily mean it's safe. What have you done with the cpcs?
It Works !!
The fact that something electrical works' does not necessarily mean it's safe. What have you done with the cpcs?
So I doubt you will get an answer to that question
 

Reply to Wiring wall lights, which is live and neutral? in the Lighting Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

Thank you, both. Seems like common sense may have prevailed, and the fellow is indeed going for one of the modern mirrors you mentioned...
Replies
3
Views
355
Brilliant. Thanks Brian much appreciate the advice.
Replies
2
Views
233

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top