Refurb on an existing building where new wet risers are going in:
Where do changeover switches for back up supplies for wet riser pumps have to be installed? Can they be installed at the main switchboar with a single cable to each pump or does the changeover switch have to ne local to the pump with 2 supply cables? Where are there regs on this?
Also I have been told by fire specialist that the supply has to be able to take the locked rotor current of all fire pumps............I have been told that 2 x 75kw pumps are going in with a LRC of 900 amps each! This seems like an unfeasable requirement ( the existing substation which supplies the building is only 1000KVA). Does this also apply to the back-up generator? Has anyone had this thrown at them before?
Any insights are welcome. Thanks
Where do changeover switches for back up supplies for wet riser pumps have to be installed? Can they be installed at the main switchboar with a single cable to each pump or does the changeover switch have to ne local to the pump with 2 supply cables? Where are there regs on this?
Also I have been told by fire specialist that the supply has to be able to take the locked rotor current of all fire pumps............I have been told that 2 x 75kw pumps are going in with a LRC of 900 amps each! This seems like an unfeasable requirement ( the existing substation which supplies the building is only 1000KVA). Does this also apply to the back-up generator? Has anyone had this thrown at them before?