Following on from another thread I have some more pictures and some more information. There are 2 questions in bold.
The customer has bought the avant rapid charger 400V/16A (moder number A426117), this is to charge the Avant Electric compact wheel loader, model e6.
The charger looks like it has a 5 pin commando plug, so I need to fit a 16A 3 phase commando socket.
Neither the charger or the loader have built in RCD protection or PEN fault protection.
The earthing system is PME for the electrical supply. The Electric vehicle is getting housed in the meter room, so I cant see any way of making the EVCP TT (to avoid Matt:e) as it will be simultaneously accessible to the many MET points in the meter room.
I plan to fit a matt:e for upstream of the commando socket, is that right? My confusion is that both Avant and the wholesaler now nothing about this. They don't have this installed for any of their chargers and I fully expect they are all protected with a type AC RCD!
Second question. Will I need a type B RCD upstream of the commando socket? Again, neither Avant nor the wholesaler had any understanding of RCD requirements. I cant see how a type A RCD will be ok as there is nothing in the literature about the charger being able to disconnect in the event of DC fault >6mA (i.e reg 722.531.2.101)
Thanks in advance
The customer has bought the avant rapid charger 400V/16A (moder number A426117), this is to charge the Avant Electric compact wheel loader, model e6.
The charger looks like it has a 5 pin commando plug, so I need to fit a 16A 3 phase commando socket.
Neither the charger or the loader have built in RCD protection or PEN fault protection.
The earthing system is PME for the electrical supply. The Electric vehicle is getting housed in the meter room, so I cant see any way of making the EVCP TT (to avoid Matt:e) as it will be simultaneously accessible to the many MET points in the meter room.
I plan to fit a matt:e for upstream of the commando socket, is that right? My confusion is that both Avant and the wholesaler now nothing about this. They don't have this installed for any of their chargers and I fully expect they are all protected with a type AC RCD!
Second question. Will I need a type B RCD upstream of the commando socket? Again, neither Avant nor the wholesaler had any understanding of RCD requirements. I cant see how a type A RCD will be ok as there is nothing in the literature about the charger being able to disconnect in the event of DC fault >6mA (i.e reg 722.531.2.101)
Thanks in advance