Laptop Power Supplies Trip RCD | on ElectriciansForums

Discuss Laptop Power Supplies Trip RCD in the UK Electrical Forum area at ElectriciansForums.net

Joined
Feb 25, 2022
Messages
6
Reaction score
0
Location
aberdeenshire
Hi,

The RCD which protects my 16A ring main always "trips" when I plug/unplug a Laptop power supply. No other type of appliance causes a problem. I have 2 laptops with the external power supplies on leads which both cause this problem. I also have a similar 240v to 12v switching adaptor for a mini fridge which will trip the RCD too.
I've had an electrician look at it but he couldn't find the problem. He replaced the RCD for the bank that the ring main is connected but it made no difference.
When the RCD trips it takes out everything on that bank including lights and heating circuit. The consumer unit has two banks protected by two separate RCD's. The MCB on the ring main appears to be working properly.

Has anyone seen anything like this? If we leave the laptop supplies plugged in permanently then there is no problem. It's only when we try to relocate the plug to a different socket that the RCD trips.

Many thanks, Archie
 
Is it the act of plugging in, or when you switch the socket on, that causes the trip?

My suspicion would be on the plug/cable of the PSU being at fault. Have you got another mains cable (assuming it is "cloverleaf" style)?
 
Is it the act of plugging in, or when you switch the socket on, that causes the trip?

My suspicion would be on the plug/cable of the PSU being at fault. Have you got another mains cable (assuming it is "cloverleaf" style)?
It's only when the plug is inserted. The socket can be on or off, it doesn't matter. I have three different power supplies that cause this problem and friends laptops cause the RCD to trip as well. I've had these cables PAT tested and they have all passed. I'm pretty confident that the fault is in the house. I've also used these cables in friends houses and they don't cause a problem there.
 
There will be EMI filters on those power supplies (see below)
The act of plugging them in (even without switching on) connects a capacitor between N and E (amongst other things).
If you aleady have leakage on that ring, the surge due to connecting the uncharged filter capacitor might just be responsible, but it's likely there is something else amiss.
If you unplug absolutely everything else from the ring, does it still do it?
[ElectriciansForums.net] Laptop Power Supplies Trip RCD
 
There will be EMI filters on those power supplies (see below)
The act of plugging them in (even without switching on) connects a capacitor between N and E (amongst other things).
If you aleady have leakage on that ring, the surge due to connecting the uncharged filter capacitor might just be responsible, but it's likely there is something else amiss.
If you unplug absolutely everything else from the ring, does it still do it?
View attachment 95438
When I unplug everything on the ring and then plug in one of the laptop power supplies it can still trip the RCD. It's not 100% repeatable though. Sometimes we can go weeks without tripping then it will happen every time we plug/unplug a supply. I think littlespark is correct and it's a cumulative earth leakage.
 
When I unplug everything on the ring and then plug in one of the laptop power supplies it can still trip the RCD. It's not 100% repeatable though. Sometimes we can go weeks without tripping then it will happen every time we plug/unplug a supply. I think littlespark is correct and it's a cumulative earth leakage.
I agree. If you could beg/borrow a sensitive clamp leakage detector, you might find what is contributing to 'cumulative'.
 
It's only when the plug is inserted.
I suspect there is, nt anything "wrong" per say. Inrush current is a feature of every electrical circuit. The natural leakage built in to the appliances you are using will also experience a momentary spike when initially plugged in. Usually rcd, s can cope with this but in your case there is obviously another (and very inconvenient) factor at play
 

Reply to Laptop Power Supplies Trip RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
357
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
389
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
446
davesparks
D
  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K
  • Question
The isolator was always going to be an unlikely option and previous information seemed to have ruled out the possibility. If I can remember...
Replies
22
Views
3K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks