Hi there

Complete novice electrical wise. I am refurbishing an old 1950s Injection Moulding machine and looking to replace the Power Timer Relays. So far with no success myself and two attempts. It appears I need some expert help. I would love direction on the type of timer I need and a link to where I could purchase is a bonus. Any help much appreciated. Details below:

The old Timers:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


What I've investigated:
  • There are 2x Timers, one for inject and one for clamp
  • They are both the same, because I can swap them around and it still runs just fine
  • Markings still remaining on one says Supply 230 V AC and Rating 6A 230 V AC. There is no cut down in power on this machine, 240V throughout.
  • They appear to be short-circuit driven (not power on all the time and Start commands etc)
  • Power is only supplied when they run and is instantly straight through to the output
  • 11 pin circular configuration
  • Phase to pin 2, Neutral to pin 10
  • Power into pin 5 and 2 makes the output run forever until short-circuited. I think I've heard this called an Inhibit function which allows the Timer to pause and force power through pin 6. In the clamp instance this forces the clamp closed, lets the inject sequence run, and then allows the Timer to run before cutting power and releasing the clamp.
  • Pin 6 is the only output. This runs to the 5/2 solenoid valves and changes the valve position for either inject or clamp
  • Timer appears to be a Power Off Delay or similar as it only tells it when to cut power off

Diagrams that I've mapped to help explain how the Timers work and current wiring:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


If you need any more info I'm happy to provide. And even if you are just interested in the machine I can post pictures of that also :)

Thanks
Murdoch
 
Interesting... will take a closer look later. Might be a silly question but if the relays work, why are you replacing them?

I am not sure what you mean by 'short-circuited' as far as the output is concerned. I would read that as a short between line and neutral that would blow the fuse, but clearly you mean something else. Can you please clarify...
 
This sounds like one that might interest Lucien!
Relays and timers, etc that use this style of plug in base are still available today, but to preserve originality, you're probably going to have to carefully open up the faulty one and see what the problem is. If beyond repair, there's plenty of room to fit a modern replacement inside the can an seal it up again'

Edit: I see I was right! Lucien has replied while I was typing this.
 
This sounds like one that might interest Lucien!
Relays and timers, etc that use this style of plug in base are still available today, but to preserve originality, you're probably going to have to carefully open up the faulty one and see what the problem is. If beyond repair, there's plenty of room to fit a modern replacement inside the can an seal it up again'

Edit: I see I was right! Lucien has replied while I was typing this.
Thanks brianmoooore, yes I've seen Lucien has replied so hope they can help :) I've tried two 11pin new timers and failed so getting the right one is the challenge
 
Interesting... will take a closer look later. Might be a silly question but if the relays work, why are you replacing them?

I am not sure what you mean by 'short-circuited' as far as the output is concerned. I would read that as a short between line and neutral that would blow the fuse, but clearly you mean something else. Can you please clarify...
Hi Lucien

Thanks for replying. Yes they do actually still work and I can run the machine through a full sequence. Unfortunately the dials and knobs and internals are all a bit knackered. So each time I come back to the machine it has vibrated and the dials moved around or if I tighten too hard it goes past and spins the case. So in short, repeatability so that when I get molds I can simply set it to 2 for example and it is 2 :)

Sorry I'm not fully up on the electrical lingo (a designer myself). But basically I'm trying to describe that there isn't power to these timers all the time like more modern versions of the 11pin. The modern ones appear to have power all the time and then trigger a start sequence. Where as these old ones appear to just get up and running once the power is applied to either 2 or 2 and 5. Then outside of itself in the sequence it is tripped and power disconnected. Does that make sense?

The two timers I have tried and failed with are:
H3CR-A (knock off version of this link below)

TR-6162U

Here's a look inside the cabinet:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


And machine if of interest:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
 
Could you tell us what is stamped on the plate circled A? See attachment.

Circled at B are the connections to pins of a device; which one? Could you show these too if they refer to the relay you wish to source new?
 

Attachments

  • [ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
    timerrelaysnz.jpg
    1.8 MB · Views: 37
Could you tell us what is stamped on the plate circled A? See attachment.

Circled at B are the connections to pins of a device; which one? Could you show these too if they refer to the relay you wish to source new?
Hi Marconi

Sure, here is a close up of the stamp and my guesses:

Type: ET P1 TIME
Ref: R1783 0.2-5 SECS
Supply: 230 V50 AC
Rating: 6A 230 V AC

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


And as for some new ones I'm wondering about there are these:

Macromatic Analag Timer TAA2U
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Autonics AT11EN
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


From my understanding the numbers 3, 4, 8, 9 are internal to the Timer. But where I struggle is, what is considered an Output and Input. Because from the looks I require Input to 5 to inhibit. And then I want 6 as the Output to the solenoid valve. I also see the - and + are the other way around on these timers.

Any help appreciated :)
 
I
Hi Marconi

Sure, here is a close up of the stamp and my guesses:

Type: ET P1 TIME
Ref: R1783 0.2-5 SECS
Supply: 230 V50 AC
Rating: 6A 230 V AC

View attachment 95470

And as for some new ones I'm wondering about there are these:

Macromatic Analag Timer TAA2U
View attachment 95471

Autonics AT11EN
View attachment 95472

From my understanding the numbers 3, 4, 8, 9 are internal to the Timer. But where I struggle is, what is considered an Output and Input. Because from the looks I require Input to 5 to inhibit. And then I want 6 as the Output to the solenoid valve. I also see the - and + are the other way around on these timers.

Any help appreciated :)
I will study these over the weekend. I have found this firm which does a wide range of 11 pin timers both electronic and mechanical. There are others of course. Just need to determine the functionality and pin out to select the correct replacements:

Foxtam Electronic Timers - Foxtam Controls - https://www.foxtamcontrols.co.uk/products/foxtam-electronic-timers?gclid=CjwKCAiAvOeQBhBkEiwAxutUVHSvHPRKJ82h19_XRP_x6cjnG9xgrFnutB03_ZHWCQ_b9qyrUHY_OhoCuRoQAvD_BwE
 
mud_the _nerd: Do you have a multimeter with an 'Ohms' range? If not could you buy a cheap digital one?

If you look at the attachment you will see two identical tables. The numbers refer to the pins on the relay. Using a multimeter please measure first the resistance between pin 1 and then to each of pins 2 to 11 of the black round timer and enter the meter reading in the table. Then do the same for pin 2 but this time to pin 1 and the each of 3 to 11. Then pin 3 but to 1 then 2 and then each of 4 to11, etcetera.

The first table is for when the timer is set to zero seconds. The second table for when it is set to say 5 seconds.

The resistance between the pins will be a low value apart from I think between pins 2 and 10.

I hope this is clear. Then return the two tables to me as an attachment.
 

Attachments

  • Connection Matrix.docx
    12.2 KB · Views: 38
Chances are that there is a modern version of what you want available, but it will likely be more sophisticated than the original, with unwanted additional functions built in. These you may have to disable, or ensure that they are not accidentally enabled.
 
Further to my last post; could you remove the black T1 and the white timer T2 and the heat relay and then take a photo of the wiring to their bases? Also take a clear picture of the terminal block so I can see which wire goes in to which terminal and to where the other ends go on the three relay bases.

Or you could do the wire tracing for me and send me a diagram. Do you have the manual for the machine with its wiring diagram inside?
 
Further to my last post; could you remove the black T1 and the white timer T2 and the heat relay and then take a photo of the wiring to their bases? Also take a clear picture of the terminal block so I can see which wire goes in to which terminal and to where the other ends go on the three relay bases.

Or you could do the wire tracing for me and send me a diagram. Do you have the manual for the machine with its wiring diagram inside?
Thanks so much for looking into this. I don't have a multimeter but I think I will buy one so I can test for you.

I actually stumbled on this article which might shed some light. It looks like timers that old might have been True Off Delay timers rather than more modern Off Delay timers. https://www.macromatic.com/blog/relays/what-is-a-true-off-delay-function

"Upon application of input voltage, the output is energized. When the input voltage is removed, the time delay (t) begins. At the end of the time delay (t), the output is de-energized. Input voltage must be applied for a minimum of 0.1 seconds to assure proper operation. Any application of the input voltage during the time delay (t) will reset the time delay. No external trigger is required."

From a search I can find some 240v 8pin ones of these. But I haven't found a 240v 11pin version. Do you know how I would test to see if a True Off Delay or not?

I do have my own attempt at a wiring diagram. I can confirm the numbers the timers are using as I took off the timers to record where the wires went:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Please keep in mind it is only the black large old timers that work. But I found some old pictures I have of inside the cabinet:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
 
I have asked FOXTAM for a quote to supply two 11 pin true delay off timers from this range:

https://www.foxtamcontrols.co.uk/assets/img/25-YRKF-8RKF-11RKF-8R2KF-11R2KF.pdf

The timer above does not require a 230V ac power supply to be present to maintain the contacts closed during the delay off period.

I will also look at other suppliers such as RS components.

I will explain later how you can use three lamps connected to the terminal strip to confirm the functionality of the timers. You do not now need to fill in the connection matrices I mentioned earlier.
 
Last edited:
murd_the_nerd:

Please remove the wires marked with a short blue dash in the attachment called 'disconnection'. Label them so you know were to connect them back to. Put the ends of these wires inside a connector so they do not touch anything. This will disconnect the valves and the heater.

Buy three neon lamps like these:

IND5032405-240-T/RD | CAMDENBOSS Red Indicator, 240V, 8mm Mounting Hole Size, Lead Wires Termination | RS Components - https://uk.rs-online.com/web/p/indicators/0576181?cm_mmc=UK-PLA-DS3A-_-google-_-CSS_UK_EN_Displays_%26_Optoelectronics_Whoop-_-Indicators_Whoop-_-576181&matchtype=&aud-832474874771:pla-302376642891&gclid=CjwKCAiAgvKQBhBbEiwAaPQw3PKQPeh7zExzTVve1WMoT2jRpbFI38x3yiulbOparbQKTL-P_mZxfxoC1tgQAvD_BwE&gclsrc=aw.ds

They are 230V ac neon indicators pre-wired with leads. Amazon will do them.

Labels these indicators as L1, L2 and L3. Now connect these lamps as I show in the second attachment 'ThreeLamps'. The leads go to the terminals at which you had disconnected a wire and the neutral.

You can now run the control panel and the lights will indicate power being supplied to the two valves or heater so that we can confirm the functionality of T1 and T2 as True Timed Delay off.
 

Attachments

  • [ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
    threelamps.jpg
    1.2 MB · Views: 37
  • [ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
    disconnections.jpg
    1,007.5 KB · Views: 40

Reply to 1950s IM Power Relay Timer Help for Solenoid Valves in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
184
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
Try disconnecting the "central heating off" wire from terminal 2 and insulate it (eg Wago connector or choc block or similar) and tuck it out of...
2 3
Replies
32
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top