Max length of cable runs. | on ElectriciansForums
Discuss Max length of cable runs. in the UK Electrical Forum area at ElectriciansForums.net
iverpool
Hi
I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs.
In some cases where there is no RCD protection the length is given as a number with a zs suffix. eg 47zs
The zs suffix means "limitted by Zs" the final circuit line-earth loop impedence.
In these cases is the number part the actual max length? For example 47zs = 47 meters?
[ElectriciansForums.net] Max length of cable runs.
Hi
ThanksView attachment 96622
Yes 47 metres max length, - but as this is due to Zs then if the Ze is bigger then normal, then obviously may be much shorter.
The "unlimited" case is voltage drop and you see it has no change between RCD/not and TN-S / TN-C-S
Most other limits are 'zs' for circuit Zs as above, however, there are a few of cases where it lists 'ad' for adiabatic limit being reached (in most cases simply not permitted, and if mentioned at any length then a reason to consider the design in more detail).
Oddly some cases just say 'NP' without a reason (e.g. 20A BS3036 with 2.5 T&E)!
Voltage drop obviously.
I'm sure if I stare at it long enough I'll spot some kind of rational pattern.
Not yet though.
Cheers
  • [ElectriciansForums.net] Max length of cable runs.
Reply to Max length of cable runs. in the UK Electrical Forum area at ElectriciansForums.net
For most domestic work the "standard circuits" in the On-Site Guide Table 7.1(ii) are all pre-checked for adequacy in these aspects, also there is...
If they are installing 32A sockets they should have additional RCD protection which makes your problem academic.
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Read up on the definitions of conductors, then circuits. Then double check what bunching is defined as - and the answer will be apparent PLUS...
I am posting an additional note in case it's useful to anyone in a similar situation: the whole thing is made more confused by the fact that I -...
4K