Hi there

Complete novice electrical wise. I am refurbishing an old 1950s Injection Moulding machine and looking to replace the Power Timer Relays. So far with no success myself and two attempts. It appears I need some expert help. I would love direction on the type of timer I need and a link to where I could purchase is a bonus. Any help much appreciated. Details below:

The old Timers:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


What I've investigated:
  • There are 2x Timers, one for inject and one for clamp
  • They are both the same, because I can swap them around and it still runs just fine
  • Markings still remaining on one says Supply 230 V AC and Rating 6A 230 V AC. There is no cut down in power on this machine, 240V throughout.
  • They appear to be short-circuit driven (not power on all the time and Start commands etc)
  • Power is only supplied when they run and is instantly straight through to the output
  • 11 pin circular configuration
  • Phase to pin 2, Neutral to pin 10
  • Power into pin 5 and 2 makes the output run forever until short-circuited. I think I've heard this called an Inhibit function which allows the Timer to pause and force power through pin 6. In the clamp instance this forces the clamp closed, lets the inject sequence run, and then allows the Timer to run before cutting power and releasing the clamp.
  • Pin 6 is the only output. This runs to the 5/2 solenoid valves and changes the valve position for either inject or clamp
  • Timer appears to be a Power Off Delay or similar as it only tells it when to cut power off

Diagrams that I've mapped to help explain how the Timers work and current wiring:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


If you need any more info I'm happy to provide. And even if you are just interested in the machine I can post pictures of that also :)

Thanks
Murdoch
 
Ahh so it appears the wiring on these is super weird having the relay output on 6! So far I haven't seen a single timer that has that. They always appear as gate, start, reset type functions. And from your notes above does that mean I wire the relay output (solenoid valve in my case) to 3 or 9 as highlighted below on a few timer variations. This timer does appear to accept power to 5 as well. Link here:

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


If you confirm above then I might finally understand these diagrams :)
 
Ahh so it appears the wiring on these is super weird having the relay output on 6! So far I haven't seen a single timer that has that. They always appear as gate, start, reset type functions. And from your notes above does that mean I wire the relay output (solenoid valve in my case) to 3 or 9 as highlighted below on a few timer variations. This timer does appear to accept power to 5 as well. Link here:

View attachment 96189

If you confirm above then I might finally understand these diagrams :)
Yes - on the 11 pin there is a set of NO contacts between terminal 1 and the circled in yellow terminals which could be used to control power to the clamp and solenoid. Your application relies on power being applied to 2 and 10 to start the timing function which determines how/when these contacts close and open. As I said we can rewire the base to use these NO contacts.

Finding a suitable replacement relay is not the current main effort - that can be done easily. What we need to confirm is what timer function is required when power is applied to 2 and 10. eg: Interval, delay on........
 
Great, then I think we've done it pretty much!

Changes would be:
  1. Change wiring as per 'After' diagram below if sticking with an 11pin timer
  2. Use a timer that starts with power input to 2 and 10
  3. Use an Interval type timer as my system continues power to input 2 past the timer ending (Interval was the only type I could see that lined up with this). I've updated the chart to represent what I'm seeing with the multimeter and ignoring 5. The flicker I eluded to before is likely the change from button power input to clamp sensor power input. And this is likely to not influence the timer as power still continuously supplied.
  4. Don't mess with any gate or start inputs. You can see in the T1 Clamp wiring it is simply folding over power to both 5 and 2 at the same time. So there really is no need for it and all the modern timers I've found need a signal input, not continuous power to 5.
From my research this is actually far more common on 8pin timers. And they are about half the price. So there could be an argument to change the 11pin to an 8pin.

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Example timing chart for Interval on an 8 pin:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
 
Your after wiring diagram needs a wire from the relay base 11 to the connector block 4 as shown in my attachment.

If you buy a couple of power (230V ac) initiated interval timers you can replace T1 and T2. If you are not sure send me a link to the ones you intend to buy and I will check they are suitable. Obviously they need to have suitable interval time range. The contacts only carry the small current to operate clamp and inject actuators. Up to you whether to go for 8 pin, 11 pin or din rail ones. Happy to check a photo before you power on should you want me to.

Please keep me informed on progress and DO NOT WORK on live equipment.

🙂
note: For power initiated interval timer if applied power goes off then interval output ends at same time.
 

Attachments

  • [ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
    1647906850506.png
    246 KB · Views: 25
Brilliant! I thought the timer power actually supplied the output power. How silly of me. But according to your diagram each Relay in the Timer can have its own power and the Timer simply switches the NC & NO contacts. So you could actually have a set up like this and mix voltages and all sorts:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


This has helped me greatly as I completely missed I need to supply power to the contacts! Thanks so much :)

I will get on to ordering some Interval Timers that function with Power ON and report back how it goes
 
And I'm thinking of going for something like this. The 8pins really are more geared to the Power On Interval style and the 11pin options are less common and expensive! The 8pin option below looks like it will do the job just fine :) One caution might be the 3A vs 6A on current Timers, is that something I should worry about? It is just supplying voltage to a solenoid valve, I can't imagine it drawing a huge amount of power.

Be thankful you don't live the next stop to Antarctica, things are hard to come by down here! The 8pin timer is in stock in Australia so quicker postage. I can get unbranded ones for $10-15 from aliexpress but figure I should get the real deal to be safe and postage can be up to a month.

AT8N
NZD$58

Spec sheet:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves



And the much more expensive 11pin option (and I'm sure others too):

TD-78121
NZD$216

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Great to be at this stage of the process and purchasing new Timers :)
 
The relay you have selected is suitable. Order AT8N . (Do not order AT8N1 or AT8N2 ).

One they have arrived we need to set up the timer range and timer mode for I = Interval operation.

You will require two 8 pin bases.

Study the connection diagram carefully for the AT8N so that you place the wires correctly to the 8 pin base.

The current switching capacity of this timer relay is satisfactory for your loads.

Also check by inspection and then with your meter on low ohms range that all items of the machine which are made of metal are indeed connected together and to the earth pin of the plug.
 
Hi Marconi. I finally had a chance to wire in the new timers today :) I was in a bit of a rush and may have got the + & - the wrong way around. The heater wouldn't start so there is an issue. I either need to force the sequence change on the machine or the wiring is not letting it turn on. There is a relay in series with the two timers (- black wires) that allows the heater to start. I ran out of time to trouble fix.

I would appreciate if you could let me know whether switching the + & - between timer pins 2 and 7 would change anything? It seems just for DC it is wired the other way. Everything else appears fine at first glance...

New wiring:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


New vs Old timers:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Timers and relay wiring new vs old:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Wiring diagram from the timer manual:
[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves
 
With power off and referring to any pictures of the relay wiring before you swapped for new ones just check you have moved the red wires to the new bases so they act as relay power or output contacts as necessary.

What do the top left and right lights do?
 
Hi Marconi. I finally had a chance to wire in the new timers today :) I was in a bit of a rush and may have got the + & - the wrong way around. The heater wouldn't start so there is an issue. I either need to force the sequence change on the machine or the wiring is not letting it turn on. There is a relay in series with the two timers (- black wires) that allows the heater to start. I ran out of time to trouble fix.

I would appreciate if you could let me know whether switching the + & - between timer pins 2 and 7 would change anything? It seems just for DC it is wired the other way. Everything else appears fine at first glance...

New wiring:
View attachment 97046

New vs Old timers:
View attachment 97047

Timers and relay wiring new vs old:
View attachment 97048

Wiring diagram from the timer manual:
View attachment 97049
It is only for dc supply you need to connect plus and minus as in the wiring diagram.
 
Thanks for confirming the +/- only being an issue for DC. No lights or anything on the timers because without the heater relay working the sequence won't even start. And power is only supplied at the time.

Hmm maybe a stuck sensor or something not to do with the timers at all. I will investigate in the coming weeks and hopefully have some good news!
 
@marconi we have victory!

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Turns out the new wiring of the timers was perfect. And the issue was with the heater relay itself. I found a loose wire, fixed that and then all worked perfectly. I don't think I can post a video on here so I've just snapshotted a picture here with the Clamp timer running and output live in interval mode. I can now see the indicator lights on and off during the sequence which is an added bonus with the new timers.

[ElectriciansForums.net] 1950s IM Power Relay Timer Help for Solenoid Valves


Thank you soo much for your help. I wouldn't have made it without you! How lucky this forum is (and me) to have you offer your expertise to problems like this 👍
 
Thank you for the update and nice comment. Would you mind taking a video using your phone and then converting it to MP4 format - there are free converters on-line - and then attach it as a file - see below - for us to see the machine in action please.

Remember there is also the check of earthing and state of cabling to be done and any other mechanical aspects to confirm as safe.
 

Reply to 1950s IM Power Relay Timer Help for Solenoid Valves in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
Try disconnecting the "central heating off" wire from terminal 2 and insulate it (eg Wago connector or choc block or similar) and tuck it out of...
2
Replies
32
Views
3K
Background I live in Indonesia, the voltage for residential buildings ranges from 220 V to 230 V, I need help with the installation of the...
Replies
0
Views
3K
If you are still interested in this, what are your electronic construction skills? I would do it exactly as @brianmoooore suggests, for which the...
Replies
11
Views
2K
nevermind... someone clued me into a genius idea that i feel like an idiot for overlooking.. I had previous looked at water pressure regulators...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks