Hi guys I’ve got a motor starter I’ve come across and looking at the electrical drawings it’s originally had 35mm tails from a 100amp fused isolator switch. This has been replaced with 25mm tri rated cable. Looking at the specs for BS 6231 I can see the conductor can take 136 amps. Motors are 37kw. Is there anything I’m missing. How do you apply grouping factors for a panel running a single motor or is grouping factors not applied?

Thanks guys
 
Treat it as any other trunking for grouping factor. Consider ambient temp on panel and how often the load will be starting and stopping
If it’s 3 phase 3xsingle core and control circuits within the trunking how does this related to how many loaded circuits? Found this in bsen 60204-1
 

Attachments

  • [ElectriciansForums.net] Tri rated cable and grouping factor
    image.jpg
    413.1 KB · Views: 2

Reply to Tri rated cable and grouping factor in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Sadly its not a great answer from your supervisor. Your motor really sets the max demand, if an overload or short cct condition arises either the...
Replies
6
Views
3K
  • Question
After fitting out the first room of downlights.... i expect him to get a bit speedier at fitting them There is so many unknowns to price at this...
2
Replies
25
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
675
There is simply too much to think about to even suggest cable sizes for this project. I must agree with my colleagues about involving an...
Replies
5
Views
2K
  • Question
Get the sparks who is going to carry out the other works to advise you
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks