Help needed trying to trace one of these neutral wires!! | on ElectriciansForums
Guest viewing is limited

Discuss Help needed trying to trace one of these neutral wires!! in the UK Electrical Forum area at ElectriciansForums.net

tommyt02

DIY
Joined
Jun 8, 2022
Messages
3
Reaction score
2
Location
Rotherham
Hello all.

I am in the process of refurbing my kitchen and I have and old redundant T&E cable coming out of the wall above one of the cabinets which I think may still be live, despite recently replacing the kitchen switch cable and chopping out the extra single & earth cable which was once a switched line to this redundant cable for the old spotlights which were boxed in above the older pine cabinets before the kitchen was refurbed in about 2011. I chopped this single and earth cable out which ran along with the original red and black T&E switch feed, but I know that there will still be a neutral running through this redundant bit of cable as the lighting circuit has a single core (red) and earth feeding the fluorescent light, along with four single neutrals running into it (one of which will be feeding this redundant cable).

What I know about the single core wiring method is that all the line conductors are fed to the switch with one going to the light in the room along with two single neutral cores running from each fitting to the last on the circuit. Because of the layout of my property, we have a porch built onto the side of our house with lighting for the downstairs toilet and utility area, but because there is no upstairs on this part, I know that one of the 3/4 neutral cores will be carrying this spur to feed the last few lights in the porch area, but the real issue is trying to find which one feeds that redundant T&E cable which will probably be junctioned in one of those old crappy JB’s to these old singles below the bathroom floor which I cannot access at all.

The real question to this is, how can I find out which black single core cable to remove which runs to this redundant cable without trying to trace it back and rip down the ceiling to find it? Will I have to do some kind of testing or is it best to call someone out to help with this? As I am going to be changing the old fluorescent fitting for a modern one soon at some point.

Any advice / help will be much appreciated!
Regards Tom
 

Attachments

  • [ElectriciansForums.net] Help needed trying to trace one of these neutral wires!!
    1454BE3D-8C57-4B06-A4FB-16C11C8BF036.jpeg
    374.1 KB · Views: 76
  • [ElectriciansForums.net] Help needed trying to trace one of these neutral wires!!
    8825CA9C-ADEA-4848-BA2F-748E3E9339E6.jpeg
    257.9 KB · Views: 55
  • [ElectriciansForums.net] Help needed trying to trace one of these neutral wires!!
    119CAFD6-55C1-42FA-8B8C-35DF2050FEAB.jpeg
    333.6 KB · Views: 56
If you have access to both ends of the cable, which it looks like you do… then a continuity test can work out which of your wires is the redundant one.
Thank you for the feedback. Do you reckon one of those cheapish digital electrical multimeters will be able to carry out the test if possible? Of course I am just trying to get to the bottom of this on a budget as I do not do electrics every day for a living - it’s just one of them small jobs I’m wanting to sort out so I can get rid of that particular cable.

Something like this I’ve attached below
 

Attachments

  • [ElectriciansForums.net] Help needed trying to trace one of these neutral wires!!
    FAFDA37D-159A-4E46-B3E2-D692D13334B5.png
    833.5 KB · Views: 41
While there are a few ways a sparks could quickly and safely identify the right wire, I wouldn't encourage a less experienced person to try and do any continuity test with the power on.

I think one safe way for the OP to do this is with a temporary length of wire. Basically with the power completely off join the temporary wire to the redundant neutral and test the other end with each of the neutrals.

A completely different approach could be to acquire some wago connectors and systematically try 3 neutrals in one wago connector and the fourth in one on it's own. Obviously the power should be off when touching any wiring. When the rest of the downstairs lights still work the one on it's own should be the redundant one.

One question though, before anything is touched. If one of the neutrals feeds a redundant T+E cable, are you confident the live is still not connected somewhere, either at a switch, a light fitting, or another hidden junction?
 
As Tim says, even if you find the N cable at both ends that you think is redundant, how can you be sure there is not something else connected to it (e.g. via a junction box) that could become live when energised, e.g. another light. I'd be wary of disconnecting it without being totally sure it is not still connected to anything else.
 
While there are a few ways a sparks could quickly and safely identify the right wire, I wouldn't encourage a less experienced person to try and do any continuity test with the power on.

I think one safe way for the OP to do this is with a temporary length of wire. Basically with the power completely off join the temporary wire to the redundant neutral and test the other end with each of the neutrals.

A completely different approach could be to acquire some wago connectors and systematically try 3 neutrals in one wago connector and the fourth in one on it's own. Obviously the power should be off when touching any wiring. When the rest of the downstairs lights still work the one on it's own should be the redundant one.

One question though, before anything is touched. If one of the neutrals feeds a redundant T+E cable, are you confident the live is still not connected somewhere, either at a switch, a light fitting, or another hidden junction?
I would never proceed to carry out a continuity test while the lighting circuit’s still live or any circuit for that matter. I’ve been doing my own electrics for a few years now and I am quite competent and understand the risks involved.
That’s also what I have recently had a thought of doing - stripping back that redundant T&E cable to temporarily connect the neutral side to a longer piece of single core cable to reach over to all the neutrals at the light and carry out the continuity test. The fluorescent tube containing all the singles is only about a meter away from this redundant cable so it should not be too much of a problem.

I do have some wago connectors in a storage compartment in my organiser from previous wiring jobs (such as the 221 levers and the push fit variety) but in my opinion it would be a bit of a pain having to repeatedly run back and forth to turn the power on and off to test and single out the redundant neutral in that fashion, but thank you for that anyways!

Im also very confident that there will no longer be a live feeding that cable above the cupboard now because before I rewired the T&E switch feed and before I ripped the old stuff out, it also had a single red and earth acting as a switched live for those old spotlights which were ripped out long ago - so that single red became completely redundant with the wire chopped off and left in the back in the box and it was not connected to the 1 gang switch which replaced the 2 gang when the kitchen was refitted 10 years ago. The previous 2 gang switch had the T&E switch cable for the main kitchen light but there was a link in the common onto the second gang with the single formerly being the switching live for those spotlights. There will definitely be a junction box hidden somewhere above the kitchen ceiling containing that red single switched live and also one of those single neutrals coming from the main light fitting which will be terminated to that redundant T&E cable, so in that respect I am highly confident there will be no current flowing through the live conductor on that bit of cable - I am more concerned about the neutral conductor now and getting it sorted!

Thanks for your help
Regards
 
As Tim says, even if you find the N cable at both ends that you think is redundant, how can you be sure there is not something else connected to it (e.g. via a junction box) that could become live when energised, e.g. another light. I'd be wary of disconnecting it without being totally sure it is not still connected to anything else.
Could they not just disconnect both ends, check continuity, then energise CU and check for an AC feed on the neutral?
 
Could they not just disconnect both ends, check continuity, then energise CU and check for an AC feed on the neutral?
There’s all sorts of things they could do. But I have two concerns
1 - there’s a limit to what I’ll advise someone to do on an Internet forum . Generally any live test is a no no. It does sound as though the OP in this case is informed and competent (and I didn’t want to suggest otherwise) but…
2 - I’m always very conscious that someone else less competent can read a thread like this and apply the advice to a completely different situation.
Hope that makes sense!
 
There’s all sorts of things they could do. But I have two concerns
1 - there’s a limit to what I’ll advise someone to do on an Internet forum . Generally any live test is a no no. It does sound as though the OP in this case is informed and competent (and I didn’t want to suggest otherwise) but…
2 - I’m always very conscious that someone else less competent can read a thread like this and apply the advice to a completely different situation.
Hope that makes sense!
I see your point
 

Reply to Help needed trying to trace one of these neutral wires!! in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Thank you so much for your help with this light work perfect now thank you again much appreciated
Replies
2
Views
288
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
667

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top