Hi All,

I have been tasked (as island resident hotel handy-man - for my sins) to replace a Emergi-lite MCP (no other details availabe) with aKAC 'MCP1' but the wiring is less than obvious, even with the MCP1's wiring leaflet. I have attached pics of each unit's innards as well as the relevant bit of the MCP1's insteuctons leaflet below. Any advice very welcome.

MW
Isle of Colonsay
Argyll
 

Attachments

  • [ElectriciansForums.net] Replacing a Fire Alarm MCP (manual call point)
    KAC MCP1 call point wiring.jpg
    80.8 KB · Views: 130
  • [ElectriciansForums.net] Replacing a Fire Alarm MCP (manual call point)
    KAC MCP1 hotel fire.JPG
    461.4 KB · Views: 81
  • [ElectriciansForums.net] Replacing a Fire Alarm MCP (manual call point)
    IMG_5783.JPG
    285.1 KB · Views: 60
Hi All,

I have been tasked (as island resident hotel handy-man - for my sins) to replace a Emergi-lite MCP (no other details availabe) with aKAC 'MCP1' but the wiring is less than obvious, even with the MCP1's wiring leaflet. I have attached pics of each unit's innards as well as the relevant bit of the MCP1's insteuctons leaflet below. Any advice very welcome.

MW
Isle of Colonsay
Argyll
hi
for future ref it doesn't matter as long as your positives and negatives are together you could have put your negs in 3 and 4 and your pos in 1 and 2 its just a switch with a 470 in it it's not polarity sensitive
 
Although you have had many suggestions, and i understand you may be the only competent person on the island... but would you working on this system invalidate any insurances the hotel owner may have if there was to be an incident.
 
Although you have had many suggestions, and i understand you may be the only competent person on the island... but would you working on this system invalidate any insurances the hotel owner may have if there was to be an incident.
Maybe, but not detecting a fire in the first place might be a bit more important when trying to explain to guests’ relatives why they were burned alive whilst waiting months for a ‘qualified engineer’ to get here - assuming one was even prepared to drive 2 hours to Oban, sit on a ferry for 2.5 hours (each way) AND spend at least a night in the (not inexpensive) hotel all to connect just 4 wires. Call me old fashioned if you will…
 
I don't work on fire alarms so this may be a daft question, but shouldn't the EOL resistor be at the end of the line? How does the panel detect an o/c on the outgoing wiring connected after that MCP? Only routine call point testing would show a fault, which could result in there being non-functioning call points when they are actually needed?
 
Last edited:
I don't work on fire alarms so this may be a daft question, but shouldn't the EOL resistor be at the end of the line? How does the panel detect an o/c on the outgoing wiring connected after that MCP? Only routine call point testing would show a fault, which could result in there being non-functioning call points when they are actually needed?
Sorry, just realised that it's not an EOL, it's in series with the switch, so I guess it's there so the panel doesn't see a short. Good job I don't touch fire alarms. :)
 

Reply to Replacing a Fire Alarm MCP (manual call point) in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top