can any one clarify if a SPD will now need to be installed when making an addition to a existing circuit? many thanks
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss will SPD protection now have to be added for an addition to an existing circuit in the UK Electrical Forum area at ElectriciansForums.net
Other conclusions are available. Like mine.From NAPIT and IET...
Its IET making our jobs more harder.Other conclusions are available. Like mine
As timhoward stated, this no longer applies.For non-residential properties that do not fit into these categories, a risk assessment must be carried out, a process that has also been simplified in the 18th edition, detailed in section 443.4 of the IET Wiring Regulations. Where this risk assessment is not conducted, the regulations require that surge protection is implemented.
It's funny. There was an era (ok a long while ago!) where it was reasonably common to add an RCD in it's own enclosure if adding a shower circuit to a rewireable board. That felt as if it was achieving something and worth doing.This is where many of us would apply the previous guidance that was given, relating to whether an RCD would need to provided when altering or adding to an existing installation.
It's funny. There was an era (ok a long while ago!) where it was reasonably common to add an RCD in it's own enclosure if adding a shower circuit to a rewireable board. That felt as if it was achieving something and worth doing.
Maybe if I could get more excited about SPDs adding value I'd be more willing to fit them in their own enclosure. But thinking about it, there are some requirements regarding lengths of conductors for SPDs that I'd have to look up again, and last time I looked into it it wasn't trivial to achieve.
Maybe if I could get more excited about SPDs adding value I'd be more willing to fit them in their own enclosure. But thinking about it, there are some requirements regarding lengths of conductors for SPDs that I'd have to look up again, and last time I looked into it it wasn't trivial to achieve.
Regs state the total length which is the line length from the OCPD to SPD + CPC length from MET to SPD should preferably not exceed 0.5m but in no case exceed 1.0m
Virtually impossible to achieve under 0.5m in an external enclosure and very difficult to achieve under 1.0m
Even internal SPDs can be difficult to achieve within these limits for a 3 phase board