Looked at a job this morning for remedial work on an EICR. The inspection has noted the plastic consumer unit within the hallway cupboard and given it a C2 rating citing regulation 422.2. The flat is on the second floor so the hallway would be the primary means of escape for the occupants.
Otherwise though it's in fine condition and sited behind a fire door in a cupboard.
What is the definition of an escape route? I can't believe that this small hallway meets the criteria as specified under reg 422.2
What do you think?
(update) I have since bothered to look further into this. Seems regulation 422.2 and the changes under amendment 2 are referring to 'protected escape routes' As the flat hallway isn't one of these then it wouldn't apply in this instance so is not a C2.