I have been asked to remove a 3 ph rcd from a vehicle entry gate, because they state it has an inverter power supply that can leak up to 160 ma .

this does not seem correct to me and i wonder of the implications of having no rcd if this leakage is to earth on touchable large metal gates.

any thoughts?
 
why Is the rcd required?
and an extra word.
For additional protection i would imagine, the rcd is already existing , the company i work for has subbed the job to another company , who have asked us to remove the rcd due to likely tripping issues.
i wonder if a type B rcd would solve the problem?
the manual for the omron 3gmx2 mentions dual independent earths so its clearly a problem ,this supply also supplies 3 lifts and water pumps ,metal conduit to metal light switches on so on.
 
If I have the right product, the manual also says:

Use an earth leakage breaker for circuit (wiring) protection between the power
supply and the main power supply terminals (R/L1, S/L2, T/L3).
An earth leakage breaker may malfunction at high frequencies as those generated
by an inverter. Use an earth leakage breaker with a large high-frequency
sensitive current rating.
When sensitivity of 30mA or even less earth leakage maybe required in certain
applications (e.g. domestic), short motor cable and convenient low-leakage
EMC filters should be selected. Check with your supplier for additional
indications.
It looks like not having one at all isn't an option.
As you said, selecting the right one seems to be the way forwards and I wouldn't be scared to phone them up and ask for advice.
 
I've just also noticed this bit:
[ElectriciansForums.net] High leakage equipment?
 
For additional protection i would imagine, the rcd is already existing
Is "additional protection" actually needed?

If it is hard wired and using SWA or similar (i.e. no vulnerable buried cables near the surface) then I don't see any requirement for a RCD, other than high Zs in a TT case. More so if you have a CPC in the SWA as well, so dual earth paths (armour and copper CPC).
 
I think additional protection is absolutely required , we know it may leak up to 160ma ,possible not all at 50hz it seems the manufacturers talk about special gfci which is an rcd by another name,it seems reckless to me to knowingly pass current down a cpc/earth
 
I think additional protection is absolutely required , we know it may leak up to 160ma ,possible not all at 50hz it seems the manufacturers talk about special gfci which is an rcd by another name,it seems reckless to me to knowingly pass current down a cpc/earth
Almost all devices pass some current down the CPC, might be microamps, might be milliamps, might even be amps if you have a big enough installation. That is why RCDs come with all sort of trip thresholds depending on what they are protecting, with the fancy MCCB incomer types often being adjustable from 30mA to 5A or more, and delays from "none" to typically 1 second or more..

For sockets with high leakage current there is/was a recommendation in the regs for dual CPC so no single point of failure in the earthing arrangement to combat the risk of an open CPC under "normal" conditions, let alone having a L-E fault at the same time.

Here you could run a 2nd CPC in parallel with the feed cable if that risk is a concern. However, I would start by looking at how it is installed and if the existing arrangement looks reliable and is not in need of "additional protection" for and cable damage contact.

.
 

Reply to High leakage equipment? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K
  • Question
Protection from what? What kind of problem with the inverter is going to be helped by having an RCD on the circuit?
Replies
5
Views
2K
davesparks
D

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top