Got a sub main board with an RCD inside. Need to test that but whenever I test it it sometimes trips the RCD from the main board. I need to test the RCD from the sub main board. Any suggestions?

My thoughts are to bypass the RCD at the main side with connector blocks momentarily but surely there is another way.
 
As above, although you have to ask about the nature of the circuit design and apparent lack of discrimination if this is so. Very few reasons to protect a standard sub-mains feed with RCD, even less if it's not a cascading system of design with variations on trip time.
 
Got a sub main board with an RCD inside. Need to test that but whenever I test it it sometimes trips the RCD from the main board. I need to test the RCD from the sub main board. Any suggestions?

My thoughts are to bypass the RCD at the main side with connector blocks momentarily but surely there is another way.
I'm not sure why that's a problem. If the downstream RCD is tripping the upstream RCD then the downstream RCD must be working. As is the upstream one. Right?
 
As above, although you have to ask about the nature of the circuit design and apparent lack of discrimination if this is so. Very few reasons to protect a standard sub-mains feed with RCD, even less if it's not a cascading system of design with variations on trip time.
It's all the rage in the air con industry.
[ElectriciansForums.net] How to test RCD when RCD is RCD protected?
 
I'm not sure why that's a problem. If the downstream RCD is tripping the upstream RCD then the downstream RCD must be working. As is the upstream one. Right?
Errmmmmm........ Nope. You know how an RCD works and what it does, yes?
 
Yes I know what an RCD does. If you have two in series and you trip #2 you're going to trip #1 as well.
You don't think so?
I don't think so, I know so. And, I'd question your knowledge of RCD's.

Hypothetically.... two commonly found 30mA AC type RCDS, in series, feeding a fixed load (with no other overload protection for the sake of making this simple...). 230v Circuit has a Zs of 0.50Ω therefore a PFC of 460A. So an earth fault occurs, 400+ Amps flows instantaneously. Which RCD goes first?
 
I don't think so, I know so. And, I'd question your knowledge of RCD's.

Hypothetically.... two commonly found 30mA AC type RCDS, in series, feeding a fixed load (with no other overload protection for the sake of making this simple...). 230v Circuit has a Zs of 0.50Ω therefore a PFC of 460A. So an earth fault occurs, 400+ Amps flows instantaneously. Which RCD goes first?

Reminds me of Matt Lucas and David Walliams

That One No!! That one.

 
The A/C units we got specified 30mA protection, even though fed in SWA, etc. They may not actually need it, but only sane option was to follow the manufacturer's instructions.

Not sure if it stems from EU markets where TT earthing is the norm?
I found this on my last commercial plant room project - AHP's were all manufacturer specified to have 30mA RCD protection (and 4p as well). I think it's a risk liability thing rather than an engineering issue.
 
Yes I know what an RCD does. If you have two in series and you trip #2 you're going to trip #1 as well.
You don't think so?

Let's say you take your MFT and test #1 at it's rated current and it trips in 19ms
You test #2 at it's rated current and it trips in 75ms
(Both times are less than the manufacturing standard requires and both would be deemed to be in fine health)

Earth leakage of exactly the rated current occurs, and RCD #1 duly trips in 19ms. Fairly clearly RCD #2 isn't going to trip, the in-balance will not be present at the coil of RCD #2 by the time it was going to trip.

Other factors include the size of the leakage current and where in the waveform cycle the fault occurs.
For these reasons on a properly designed system each additional RCD's in series needs have 'l delta n' (trip current) at least 3x greater than the previous RCD guarantee selectivity.
 
So I would connect the live to the live outgoing of RCD, the neutral to the neutral outgoing of the RCD and the earth to the neutral incoming of RCD?
Connect your MFT earth lead to the neutral feeding the 2nd RCD.

That way it diverts the current around it so it should see the fault and trip, but the up-stream RCD sees nothing unusual
 
The A/C units we got specified 30mA protection, even though fed in SWA, etc. They may not actually need it, but only sane option was to follow the manufacturer's instructions.

Not sure if it stems from EU markets where TT earthing is the norm?
Somewhere on here I quoted a response I got from Daikin who specified type B RCD protection.

There response was something along the lines of "yeah, that's standard wording o. All quotes but we'll accept installation to local code" 😂

Which was a relief as a three phase type B RCD is upwards of £600, and I needed eight of them...
 
As above, although you have to ask about the nature of the circuit design and apparent lack of discrimination if this is so. Very few reasons to protect a standard sub-mains feed with RCD, even less if it's not a cascading system of design with variations on trip time.
Been thinking a lot about your comment. Shouldn't the cable that's being fed from the main board to the sub main be RCD protected?
 

Reply to How to test RCD when RCD is RCD protected? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
Replies
17
Views
529
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
402
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
637
Ok I’ll try this when I’m down
Replies
4
Views
286
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks