Hello,

Question is regarding a recently purchased property in Central Texas, which includes a 27KW tankless electric water heater. It is four years old and working fine.

What the prior owner installed is surely not code compliant, but the county does not require permitting for "renovations made within the original square footage of buildings".

The subpanel breakers next to the water heater are essentially nearby cutoff switches. The main panel is 80 feet away.

Aside from the code, is there anything electrically wrong with this setup that it would make good sense to (1) replace the wiring to subpanel or (2) remove the subpanel completely?


[ElectriciansForums.net] Paralleling 8-gauge wires to a 220V Subpanel for Tankless Water Heater

t
 
I would be looking at removing the sub panel, it looks to be reducing safety rather than improving it.
have you spoken to any local electricians?
 
I would be looking at removing the sub panel, it looks to be reducing safety rather than improving it.
have you spoken to any local electricians?
Thanks. I spoke with a couple of experienced electricians in a large electronics manufacturing plant I work at. Neither saw anything "wrong" per se with the setup from a purely electrical circuit point of view. Just looking to see if anyone has a solid argument beyond "doesn't look right"
 
The thing wrong is someone could expect that turning off one of the outgoing breakers in the main panel would make the outgoing terminals dead, in this case they would remain live.

in the U.K. if you are running cables in parallel then they need to be fed from the same circuit breaker. (Amongst other requirements)
 
B
Hello,

Question is regarding a recently purchased property in Central Texas, which includes a 27KW tankless electric water heater. It is four years old and working fine.

What the prior owner installed is surely not code compliant, but the county does not require permitting for "renovations made within the original square footage of buildings".

The subpanel breakers next to the water heater are essentially nearby cutoff switches. The main panel is 80 feet away.

Aside from the code, is there anything electrically wrong with this setup that it would make good sense to (1) replace the wiring to subpanel or (2) remove the subpanel completely?


View attachment 100096
t
By Code you are not allowed to parallel nothing under 1/0 wire, and that’s a big tankless water heater. You wire size needs to be # 3 at a minimum. My mission is to tell you the correct answer to your question by code. You live where you live and if code enforcement doesn’t care then all I can say is good luck with your project
 

Reply to Paralleling 8-gauge wires to a 220V Subpanel for Tankless Water Heater in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top