I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps.
The distribution circuits will be fed in 6mm mostly for VD reasons but also to allow some selectivity on the OCPD(MCB) my dilemma is SWA or T&E.
The route is 98% tray before entering a room and feeding a surface mounted consumer unit.
For aesthetic reasons they want the cables in the wall, fair enough, but I'm in a catch 22.
If SWA I'd never be able to gland into the back of the CUs and the SWA would end up surface, if T&E the cable would be in a timber partition but less that 50mm deep thus requiring RCD which completely negates the principle of sub devision of circuits.
1, Am I going OTT worrying about this c0.5m drop from the ceiling to the back of the CU?
2, My "Solution" is to mount a galvanised box above the ceiling, gland the T&E through into some earthed steel flexicon, down inside the wall and into the back of the CU.
3, Am I missing a more obvious simpler solution?
Thanks.
The distribution circuits will be fed in 6mm mostly for VD reasons but also to allow some selectivity on the OCPD(MCB) my dilemma is SWA or T&E.
The route is 98% tray before entering a room and feeding a surface mounted consumer unit.
For aesthetic reasons they want the cables in the wall, fair enough, but I'm in a catch 22.
If SWA I'd never be able to gland into the back of the CUs and the SWA would end up surface, if T&E the cable would be in a timber partition but less that 50mm deep thus requiring RCD which completely negates the principle of sub devision of circuits.
1, Am I going OTT worrying about this c0.5m drop from the ceiling to the back of the CU?
2, My "Solution" is to mount a galvanised box above the ceiling, gland the T&E through into some earthed steel flexicon, down inside the wall and into the back of the CU.
3, Am I missing a more obvious simpler solution?
Thanks.