Hi all,

After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth.

I believe it to be a TN-S as the main earth is attached to the back of the main incoming cable. In December, I got the CU replaced and isolator fitted and was advised by an electrician that cut-out replacements would alter the earthing system to TN-C-S or PME.

This morning, the DNO dug up the pavement (assuming they cut the cable) and reconnected after the replacement. However, the main earth was not touched at all. It is 4mm2 cable that goes behind the incoming cable is just stuck to the wall with no earth clamp.

The DNO measured the earth impedance using the live and neutral and quoted it was 0.3 with the maximum allowed is 0.8

I've attached photos. In the photos, you see two earths, the larger earth leads outside to the gas pipe, the smaller earth goes behind the incoming cable. Also, notice that the fuse carrier is not sealed.

Any advice much appreciated.
 

Attachments

  • [ElectriciansForums.net] Main earth after cut-out replacement
    IMG_20220815_151129.jpg
    230.2 KB · Views: 130
  • [ElectriciansForums.net] Main earth after cut-out replacement
    IMG_20220815_160421.jpg
    202.4 KB · Views: 114
  • [ElectriciansForums.net] Main earth after cut-out replacement
    IMG_20220815_151129.jpg
    230.2 KB · Views: 111
Last edited:
I believe it to be a TN-S as the main earth is attached to the back of the main incoming cable.
Correct
In December, I got the CU replaced and isolator fitted and was advised by an electrician that cut-out replacements would alter the earthing system to TN-C-S or PME.
That would have been a fair guess, but it was a wrong guess as things turned out. No big deal.
This morning, the DNO dug up the pavement (assuming they cut the cable) and reconnected after the replacement. However, the main earth was not touched at all. It is 4mm2 cable that goes behind the incoming cable is just stuck to the wall with no earth clamp.
I think it is actually brazed to the lead cable. Rather difficult to say from photo.
The DNO measured the earth impedance using the live and neutral and quoted it was 0.3 with the maximum allowed is 0.8
I'm assuming/hoping they also had the test device connected to the 4mm earth wire with it disconnected from the metal MET block.
If so that's a good result and proves a decent connection.

As far as I can see, whether it's a 60 or 80A fuse in the cut-out, the regs are satisfied (adiabatic equiation) with a 4mm earth.
Worst case (lower limit) fault current of 766A . The max prospective fault current will be higher as the neutral is bigger, lower impedance = higher current = faster trip time.

For 766A fault current, 60A disconnection time is 0.2s. 80 disconnection time is 0.7s.
I get between 3mm (so 4mm) for 60A and 4mm for 80A.
At this point I'm not concerned.

If you have concerns it's a quick job to have a sparks verify the Ze (earth impendence).
 
Correct

That would have been a fair guess, but it was a wrong guess as things turned out. No big deal.

I think it is actually brazed to the lead cable. Rather difficult to say from photo.

I'm assuming/hoping they also had the test device connected to the 4mm earth wire with it disconnected from the metal MET block.
If so that's a good result and proves a decent connection.

As far as I can see, whether it's a 60 or 80A fuse in the cut-out, the regs are satisfied (adiabatic equiation) with a 4mm earth.
Worst case (lower limit) fault current of 766A . The max prospective fault current will be higher as the neutral is bigger, lower impedance = higher current = faster trip time.

For 766A fault current, 60A disconnection time is 0.2s. 80 disconnection time is 0.7s.
I get between 3mm (so 4mm) for 60A and 4mm for 80A.
At this point I'm not concerned.

If you have concerns it's a quick job to have a sparks verify the Ze (earth impendence).
Would they still have maintained the TN-S supply after reconnecting?

By reconnecting I mean cutting and rejoining.
 
Last edited:
Cant do anything about the size of the main earth the DNO supply. We're only concerned about the consumer side not the supply side. If the supply company have tested their side and say that's the reading their getting then we have to go with that If your worried get it tested but its probably fine.
 

Reply to Main earth after cut-out replacement in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
1K
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3
Replies
68
Views
4K
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
945
  • Question
Indeed it is clearly marked as a PME earthing system, which means it is TNCS.
Replies
5
Views
3K
loz2754
L
  • Question
Thanks all. Im back there tomorrow, and hopefully be able to trace back earth cable.
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks