After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth.
I believe it to be a TN-S as the main earth is attached to the back of the main incoming cable. In December, I got the CU replaced and isolator fitted and was advised by an electrician that cut-out replacements would alter the earthing system to TN-C-S or PME.
This morning, the DNO dug up the pavement (assuming they cut the cable) and reconnected after the replacement. However, the main earth was not touched at all. It is 4mm2 cable that goes behind the incoming cable is just stuck to the wall with no earth clamp.
The DNO measured the earth impedance using the live and neutral and quoted it was 0.3 with the maximum allowed is 0.8
I've attached photos. In the photos, you see two earths, the larger earth leads outside to the gas pipe, the smaller earth goes behind the incoming cable. Also, notice that the fuse carrier is not sealed.
Any advice much appreciated.
After months of waiting, the fused neutral cut-out at my parents house has been replaced but I am concerned about the main earth.
I believe it to be a TN-S as the main earth is attached to the back of the main incoming cable. In December, I got the CU replaced and isolator fitted and was advised by an electrician that cut-out replacements would alter the earthing system to TN-C-S or PME.
This morning, the DNO dug up the pavement (assuming they cut the cable) and reconnected after the replacement. However, the main earth was not touched at all. It is 4mm2 cable that goes behind the incoming cable is just stuck to the wall with no earth clamp.
The DNO measured the earth impedance using the live and neutral and quoted it was 0.3 with the maximum allowed is 0.8
I've attached photos. In the photos, you see two earths, the larger earth leads outside to the gas pipe, the smaller earth goes behind the incoming cable. Also, notice that the fuse carrier is not sealed.
Any advice much appreciated.