Hi to all,

I am struggling to connect up extractor fan Helios ELS-VNC 100. I would like that fan to be switched with lighting circuits and overrun for 6 minutes. Could you advise which terminals should be used for connection please?
Could you explain difference with operation by terminal 1 and terminal 3 please?

Thanks
 
That's a nice sophisticated fan you have there!
For what you want, you just need to connect permanent L and N to the terminals marked as such, and connect the L from the light to terminal 3.

[ElectriciansForums.net] Extractor Fan Helios ELS-VNC 100 connection
Pin 1 is to connect a switch to turn off the automatic function. I don't think you need to connect anything to that.
The application of L to pin 3 (ie turning on the light) is what will start the fan. The removal of L from pin 3 (ie turning off the light) will start the interval timer, and the fan then runs for 6 minutes (default factory setting) using the permanent L feed.

The timer period is selected by DIP switches, along with some other parameters. Sounds like you need to set the switches before you finally install the fan.

[ElectriciansForums.net] Extractor Fan Helios ELS-VNC 100 connection
 

Reply to Extractor Fan Helios ELS-VNC 100 connection in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

  • Question
I'm familiar with many domestic extractor fans which are primarily class 2 (double insulated) and consequently are not required to be earthed...
Replies
13
Views
2K
  • Question
I think you are going to need an electrician because it looks like someone has used the bare earth (has been sleeved black) as a live conductor...
Replies
1
Views
895

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top