During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?
 
[ElectriciansForums.net] Meter tails no rcd in stud wall
 
As above I hate meter tails being snaked through a wall cavity or run up inside a stud wall with no way of knowing where they are actually sited

Made even worse if there is no RCD protection
 
Are the tails definitely bare in the stud wall, or is it possible they have mechanical protection, complying with 522.6.204, (which I think would mean no RCD req'd)?

I have come across this a few years back in a new build, when putting up a cabinet in a toilet. The tails were installed in a steel stud wall, and my magnet picked up the mechanical protection. Thinking it was just another steel stud, I tried drilling it for a couple of minutes, before realising something was amiss and checked the other side of the wall to find the CU there!
 
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?
As @Pretty Mouth has said in his post. I have twice now installed tails like this, both times I have used mechanical protection (3mm steel) which may not be visible without chiselling a bit of the wall out.
 
During an EICR meter tails were found entering the cavity and coming down a stud wall to a consumer unit about 5 meters (direct distance) away.
they do have an isolator but no rcd or other protection .

as cables buried in a wall have to have (RCD) Residual Current Device at 30mA and generally tails over 3 meters are not permitted by DNO ,how can this comply?

Cables buried in a wall don't have to have RCD protection, they can have other forms of protection.

As you are carrying out an EICR it is very difficult to confirm whether or not correct protection has been installed. Examination of cables buried within walls, under floors etc is a standard limitation.

You need to make a judgement call as to whether it is likely to comply or not. When was it installed, what is the general standard of the installation, what records are available?
 
I watched that efixx vid, and re-watched it a couple of times, and then had a read through the regs mentioned.

433.3.1(iii), 434.3 (iv), and item (ii) of 434.2.1, these make me think that the tails are not restricted to 3m, as long as they are well protected mechanically, and that the DNO agrees that they are protected by their fuse.

Does anyone know under what circumstances a DNO would agree, or even disagree, to this?
 
I watched that efixx vid, and re-watched it a couple of times, and then had a read through the regs mentioned.

433.3.1(iii), 434.3 (iv), and item (ii) of 434.2.1, these make me think that the tails are not restricted to 3m, as long as they are well protected mechanically, and that the DNO agrees that they are protected by their fuse.

Does anyone know under what circumstances a DNO would agree, or even disagree, to this?

They'll probably never agree to it, certainly not for small supplies.
I've found that DNO's generally allow between 3 and 4 metres of tails maximum.
 
thanks for all the interesting input and advice, i also put the same question to NICEIC but im less than impressed with the reply:



Good Afternoon,

Thank You For Your Enquiry

Based on the information provided, our guidance is as follows;

There is not a specific regulation within BS7671 which states whether or not supply tails with no RCD protection with a length of run greater than 3metres would result in a satisfactory or unsatisfactory outcome.

Do you feel that there is a safety concern or do you feel that an improvement can be made? Please could you also clarify how the tails have been installed.

Once we get further clarification from yourself than we may be able to assist further with your query.

Regards,
 
thanks for all the interesting input and advice, i also put the same question to NICEIC but im less than impressed with the reply:



Good Afternoon,

Thank You For Your Enquiry

Based on the information provided, our guidance is as follows;

There is not a specific regulation within BS7671 which states whether or not supply tails with no RCD protection with a length of run greater than 3metres would result in a satisfactory or unsatisfactory outcome.

Do you feel that there is a safety concern or do you feel that an improvement can be made? Please could you also clarify how the tails have been installed.

Once we get further clarification from yourself than we may be able to assist further with your query.

Regards,
Their response doesn't seem unreasonable. DNO conditions of supply and BS 7671 requirements are separate issues. It doesn't mean that the installation is not in breach of the former, however.
 

Reply to Meter tails no rcd in stud wall in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for the replies, I appreciate it.
Replies
4
Views
558
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
641
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
831
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
487
  • Question
For anyone interested, I tested the supply side RCBO today and got a 1x I time of <130ms, so I don't believe it is a Type S. I did however have...
Replies
12
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks