Hi everyone, my husband has turned up on a job with a very old mains that he will need to shut down at some stage. Does anyone know the procedure for shutting down/re starting this type of mains? Photos attached. Apologies if this is the wrong forum and thanks for reading!
[ElectriciansForums.net] English Electric Mains shut down/start up procedure
[ElectriciansForums.net] English Electric Mains shut down/start up procedure
 
Hi everyone, my husband has turned up on a job with a very old mains that he will need to shut down at some stage. Does anyone know the procedure for shutting down/re starting this type of mains? Photos attached. Apologies if this is the wrong forum and thanks for reading!View attachment 101397View attachment 101398

There is not enough information there.

It's clearly an ACB, and it looks like an old EE E3, which could be 3.3kV.

If he doesn't know how to operate any item of switchgear, he should be nowhere near it.


EE used the same or similar facia for most of their range, only really adding more information/options as they got higher in voltage, by the time you get to the E7 & E8 they do look significantly different to the lower voltage stuff.

This could be a 415V or 3.3kV ACB.

Edit.

If it is 415V it could be the M-pact range, likely in a form 4 switchboard, but there is no way to be sure from these photos.
 
Last edited:
There is not enough information there.

It's clearly an ACB, and it looks like an old EE E3, which could be 3.3kV.

If he doesn't know how to operate any item of switchgear, he should be nowhere near it.


EE used the same or similar facia for most of their range, only really adding more information/options as they got higher in voltage, by the time you get to the E7 & E8 they do look significantly different to the lower voltage stuff.

This could be a 415V or 3.3kV ACB.

Edit.

If it is 415V it could be the M-pact range, likely in a form 4 switchboard, but there is no way to be sure from these photos.

There is not enough information there.

It's clearly an ACB, and it looks like an old EE E3, which could be 3.3kV.

If he doesn't know how to operate any item of switchgear, he should be nowhere near it.


EE used the same or similar facia for most of their range, only really adding more information/options as they got higher in voltage, by the time you get to the E7 & E8 they do look significantly different to the lower voltage stuff.

This could be a 415V or 3.3kV ACB.

Edit.

If it is 415V it could be the M-pact range, likely in a form 4 switchboard, but there is no way to be sure from these photos.
Thanks for your help, unfortunately there is no other information available.

He would not work on an item that he does not know how to operate, hence my asking for information - we're trying to find someone that has worked on these to assist - we've drawn a blank so far but hopefully your additional information may help, so thanks again.
 
Thanks for your help, unfortunately there is no other information available.

He would not work on an item that he does not know how to operate, hence my asking for information - we're trying to find someone that has worked on these to assist - we've drawn a blank so far but hopefully your additional information may help, so thanks again.

It is pretty important you get the right information, English Electric made the OB3 in the 1950s - this MUST NOT BE OPERATED!

It was redesigned to be the M-pact in the 60s and EE got swallowed up by GEC in the late 60s, after this the M-pact became the GEC M-pact (now known as the mk 1) since then it's become the mk2, new M-pact, M-pact plus etc.

The ob3 and M-pact mk1 look similar when you just have the small view as your photo.
 
Hi everyone, my husband has turned up on a job with a very old mains that he will need to shut down at some stage. Does anyone know the procedure for shutting down/re starting this type of mains? Photos attached. Apologies if this is the wrong forum and thanks for reading!View attachment 101397View attachment 101398
Hello Katie.
Tell your husband not to touch it. There is almost certainly high energy present (arc flash hazard); it should have been risk-assessed and labelled as such. If so, that means arc-rated PPE is essential to safely operate this circuit breaker. The lack of arc flash labelling and circuit designation labels leads me to think it has not been maintained. If the site owner does not know how to operate it, it may not have been functioned for an unknown period of time and may be unsafe. Call the DNO; they have all the right PPE to deal with it and will also be able to service and test it, which will be required. It then needs to go on a routine maintenance schedule and be risk-assessed for the potential arc flash hazard. And, usually, the lower the service voltage, the greater the arc flash hazard, so don't relax if it's found to be "only" 415 volts. Keep well away from it in the interim.
Regards,
Colin Jenkins.
 
Surely, if it's MV switchgear then the owner would know if they have a massive buzzing TX somewhere?!
 
It is pretty important you get the right information, English Electric made the OB3 in the 1950s - this MUST NOT BE OPERATED!

It was redesigned to be the M-pact in the 60s and EE got swallowed up by GEC in the late 60s, after this the M-pact became the GEC M-pact (now known as the mk 1) since then it's become the mk2, new M-pact, M-pact plus etc.

The ob3 and M-pact mk1 look similar when you just have the small view as your photo.
Thank you, he is going to contact the DNO, thanks for all your advice.
 
Hello Katie.
Tell your husband not to touch it. There is almost certainly high energy present (arc flash hazard); it should have been risk-assessed and labelled as such. If so, that means arc-rated PPE is essential to safely operate this circuit breaker. The lack of arc flash labelling and circuit designation labels leads me to think it has not been maintained. If the site owner does not know how to operate it, it may not have been functioned for an unknown period of time and may be unsafe. Call the DNO; they have all the right PPE to deal with it and will also be able to service and test it, which will be required. It then needs to go on a routine maintenance schedule and be risk-assessed for the potential arc flash hazard. And, usually, the lower the service voltage, the greater the arc flash hazard, so don't relax if it's found to be "only" 415 volts. Keep well away from it in the interim.
Regards,
Colin Jenkins.
Thanks so much, he is contacting the DNO as suggested. Really appreciate the help.
 
A wise move. Thanks for reassuring us.

A key point here is that an ACB of this type, is not something that you just operate without forethought. Even if you are skilled and familiar with the equipment, the procedure used needs to take account of the local conditions, maintenance status or lack of it, load being interrupted, prospect of closing onto a fault etc, all of which would be built into the risk assessment for the activity.

These things can be deceptive. They sit quietly for decades giving an impression of solid reliability, but without actually being called upon to perform their job and without the maintenance necessary to keep them ready to spring into action. Then, when someone finally presses the button and the neglected mechanism malfunctions, it erupts into a fireball.
 
Then, when someone finally presses the button and the neglected mechanism malfunctions, it erupts into a massive viral hit on Youtube.
Corrected that for you.
 
A wise move. Thanks for reassuring us.

A key point here is that an ACB of this type, is not something that you just operate without forethought. Even if you are skilled and familiar with the equipment, the procedure used needs to take account of the local conditions, maintenance status or lack of it, load being interrupted, prospect of closing onto a fault etc, all of which would be built into the risk assessment for the activity.

These things can be deceptive. They sit quietly for decades giving an impression of solid reliability, but without actually being called upon to perform their job and without the maintenance necessary to keep them ready to spring into action. Then, when someone finally presses the button and the neglected mechanism malfunctions, it erupts into a fireball.

If it is an OB3 it would be dependent manual operation.

Which means it closes as slowly as you operate it!

People have been known to start opening them, halfway through closing them because they hear arcing.

It does indeed turn into a fireball.

M-pact and the E series could be independent manual, manual charged spring, motor charged spring, or solenoid.
 
To give a small example, this is a test where I applied a small fault to a piece of switchgear with a minor manufacturing fault (deliberate), the piece of heat sensitive board to the front-left of the switchgear is the size and in the place where the operator would be when operating it.
[ElectriciansForums.net] English Electric Mains shut down/start up procedure

[ElectriciansForums.net] English Electric Mains shut down/start up procedure

[ElectriciansForums.net] English Electric Mains shut down/start up procedure

[ElectriciansForums.net] English Electric Mains shut down/start up procedure

[ElectriciansForums.net] English Electric Mains shut down/start up procedure

[ElectriciansForums.net] English Electric Mains shut down/start up procedure



Unfortunately although you can see the "operator" pushed back, the angle obscures the view - the material was burnt right through in places, indicating the operator could have suffered 3rd/4th degree burns to 75/40% of their body.
 
Last edited:
What are those disc things all around the room. In fact, what is that room? @Julie. And, errr, I have made a solemn promise to myself to not operate an air circuit breaker anytime soon!
P.S. And why must the OB3 NOT BE OPERATED? Is/was it defective like the above? All very interesting by the way.
 
Last edited:
What are those disc things all around the room. In fact, what is that room? @Julie. And, errr, I have made a solemn promise to myself to not operate an air circuit breaker anytime soon!

Look like insulators with bus bars mounted on them I think? Looks very interesting eh!
 
To give a small example, this is a test where I applied a small fault to a piece of switchgear with a minor manufacturing fault (deliberate), the piece of heat sensitive board to the front-left of the switchgear is the size and in the place where the operator would be when operating it.
View attachment 101428
View attachment 101429
View attachment 101430
View attachment 101431
View attachment 101432
View attachment 101433


Unfortunately although you can see the "operator" pushed back, the angle obscures the view - the material was burnt right through in places, indicating the operator could have suffered 3rd/4th degree burns to 75/40% of their body.

You've broken that.
 
P.S. And why must the OB3 NOT BE OPERATED? Is/was it defective like the above? All very interesting by the way.
I think it is the "dependant operation" aspect, in other words unless you can and know how to make the damn thing operate VERY QUICKLY you get a serious arc-flash/arc-blast risk.

I'm not even sure if that is allowed any more?
 
A quick search finds this useful document:

I has the requirements on page4 of:
  • prohibiting the operation of dependent manually-operated switchgear when live, except under very carefully controlled conditions;
And just below that:
  • when possible, replacing the closing mechanism for dependent manually-operated switchgear. When this is not possible, you must replace the switchgear;
 
People have been known to start opening them, halfway through closing them because they hear arcing.

To use a flight analogy, it's like trying to abort a takeoff after V1, which you only do if the aircraft is incapable of flight. It is better to continue, even if you suspect there is a problem, than to create a worse one by aborting. In an aircraft that would be a runway excursion, with switchgear it's the aforementioned fireball.

Operating open front switchgear on 250-500V DC at lower currents, you can get a clear idea of how an arc behaves according to what you do with the switch handle, without the risk of the severe arc-flash injury that comes with failed MV or HV or even high current LV switching events. IMO every electrical apprentice should get to see and feel this.
 
What are those disc things all around the room. In fact, what is that room? @Julie. And, errr, I have made a solemn promise to myself to not operate an air circuit breaker anytime soon!
P.S. And why must the OB3 NOT BE OPERATED? Is/was it defective like the above? All very interesting by the way.

The red Yellow and blue busbars are the three phases we connected the equipment to, we could choose the voltage on those from 200V to 38kV depending upon the test requirements, the disks are insulators.

That is a test bay at a switchgear testing station, low - medium voltage, unfortunately I don't have photos of the other bays some of which go to high voltage (66kV+)

The OB3 operates like many of the era and is known as "dependant manual"

This means the speed of contact closure is completely dependent upon the operator, if you are hesitant and do it slowly or even stop and reverse, then the contacts will not make properly.

Switchgear is generally designed to close onto a fault, but opening a fault is not always required (switches), and when it is able to interrupt a fault (breaker), they sometimes use different contacts, and in any case they always need to follow the proper cycle from: contact made, contact separation, arc, arc control, then arc extinction then fully open.

Dependant manual interrupts this cycle.

As long as you make a swift closure, even on to a fault, the breaking cycle can complete safely.

As you may guess I worked at both a switchgear manufacturer and testing station , unfortunately I had to go out and investigate some incidents including a number where deaths had been involved.

I did attend one where an operator had started to close a switch (~11kV) designed in the late '40s manufactured in the 50s - so dependant manual, and realised he hadn't removed the earth links, so hesitated half way through and tried to open it.

5 out of the 6 people in the switchroom died, the one who lived was near the door managed to get out but was engulfed in the burning oil, it was horrific to be honest, one of the worst I investigated.
 
The red Yellow and blue busbars are the three phases we connected the equipment to, we could choose the voltage on those from 200V to 38kV depending upon the test requirements, the disks are insulators.

That is a test bay at a switchgear testing station, low - medium voltage, unfortunately I don't have photos of the other bays some of which go to high voltage (66kV+)

The OB3 operates like many of the era and is known as "dependant manual"

This means the speed of contact closure is completely dependent upon the operator, if you are hesitant and do it slowly or even stop and reverse, then the contacts will not make properly.

Switchgear is generally designed to close onto a fault, but opening a fault is not always required (switches), and when it is able to interrupt a fault (breaker), they sometimes use different contacts, and in any case they always need to follow the proper cycle from: contact made, contact separation, arc, arc control, then arc extinction then fully open.

Dependant manual interrupts this cycle.

As long as you make a swift closure, even on to a fault, the breaking cycle can complete safely.

As you may guess I worked at both a switchgear manufacturer and testing station , unfortunately I had to go out and investigate some incidents including a number where deaths had been involved.

I did attend one where an operator had started to close a switch (~11kV) designed in the late '40s manufactured in the 50s - so dependant manual, and realised he hadn't removed the earth links, so hesitated half way through and tried to open it.

5 out of the 6 people in the switchroom died, the one who lived was near the door managed to get out but was engulfed in the burning oil, it was horrific to be honest, one of the worst I investigated.

That's really scary that.
 

Reply to English Electric Mains shut down/start up procedure in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Haha! Normally I would sweat just reading those posts! I'm not that steady on my feet when I'm standing on the ground, so ladders are hateful for...
    • Like
Replies
3
Views
264
D
  • Question
The revised arrangement - please check that I have fully understood the points made in the above threads. Obviously a qualified electrician will...
Replies
5
Views
3K
Deleted member 155212
D
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D
  • Question
I am posting an additional note in case it's useful to anyone in a similar situation: the whole thing is made more confused by the fact that I -...
Replies
11
Views
4K
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks