Hi everyone, my husband has turned up on a job with a very old mains that he will need to shut down at some stage. Does anyone know the procedure for shutting down/re starting this type of mains? Photos attached. Apologies if this is the wrong forum and thanks for reading!View attachment 101397View attachment 101398
There is not enough information there.
It's clearly an ACB, and it looks like an old EE E3, which could be 3.3kV.
If he doesn't know how to operate any item of switchgear, he should be nowhere near it.
EE used the same or similar facia for most of their range, only really adding more information/options as they got higher in voltage, by the time you get to the E7 & E8 they do look significantly different to the lower voltage stuff.
This could be a 415V or 3.3kV ACB.
Edit.
If it is 415V it could be the M-pact range, likely in a form 4 switchboard, but there is no way to be sure from these photos.
Thanks for your help, unfortunately there is no other information available.There is not enough information there.
It's clearly an ACB, and it looks like an old EE E3, which could be 3.3kV.
If he doesn't know how to operate any item of switchgear, he should be nowhere near it.
EE used the same or similar facia for most of their range, only really adding more information/options as they got higher in voltage, by the time you get to the E7 & E8 they do look significantly different to the lower voltage stuff.
This could be a 415V or 3.3kV ACB.
Edit.
If it is 415V it could be the M-pact range, likely in a form 4 switchboard, but there is no way to be sure from these photos.
Thanks for your help, unfortunately there is no other information available.
He would not work on an item that he does not know how to operate, hence my asking for information - we're trying to find someone that has worked on these to assist - we've drawn a blank so far but hopefully your additional information may help, so thanks again.
Hello Katie.Hi everyone, my husband has turned up on a job with a very old mains that he will need to shut down at some stage. Does anyone know the procedure for shutting down/re starting this type of mains? Photos attached. Apologies if this is the wrong forum and thanks for reading!View attachment 101397View attachment 101398
Thank you, he is going to contact the DNO, thanks for all your advice.It is pretty important you get the right information, English Electric made the OB3 in the 1950s - this MUST NOT BE OPERATED!
It was redesigned to be the M-pact in the 60s and EE got swallowed up by GEC in the late 60s, after this the M-pact became the GEC M-pact (now known as the mk 1) since then it's become the mk2, new M-pact, M-pact plus etc.
The ob3 and M-pact mk1 look similar when you just have the small view as your photo.
Thanks, he is contacting the DNO, really appreciate your help.I've used some later descendants - GE M-Pact motor wound spring (MWS) units. The post above says it all, don't do it!
Thanks so much, he is contacting the DNO as suggested. Really appreciate the help.Hello Katie.
Tell your husband not to touch it. There is almost certainly high energy present (arc flash hazard); it should have been risk-assessed and labelled as such. If so, that means arc-rated PPE is essential to safely operate this circuit breaker. The lack of arc flash labelling and circuit designation labels leads me to think it has not been maintained. If the site owner does not know how to operate it, it may not have been functioned for an unknown period of time and may be unsafe. Call the DNO; they have all the right PPE to deal with it and will also be able to service and test it, which will be required. It then needs to go on a routine maintenance schedule and be risk-assessed for the potential arc flash hazard. And, usually, the lower the service voltage, the greater the arc flash hazard, so don't relax if it's found to be "only" 415 volts. Keep well away from it in the interim.
Regards,
Colin Jenkins.
Corrected that for you.Then, when someone finally presses the button and the neglected mechanism malfunctions, it erupts into a massive viral hit on Youtube.
A wise move. Thanks for reassuring us.
A key point here is that an ACB of this type, is not something that you just operate without forethought. Even if you are skilled and familiar with the equipment, the procedure used needs to take account of the local conditions, maintenance status or lack of it, load being interrupted, prospect of closing onto a fault etc, all of which would be built into the risk assessment for the activity.
These things can be deceptive. They sit quietly for decades giving an impression of solid reliability, but without actually being called upon to perform their job and without the maintenance necessary to keep them ready to spring into action. Then, when someone finally presses the button and the neglected mechanism malfunctions, it erupts into a fireball.
What are those disc things all around the room. In fact, what is that room? @Julie. And, errr, I have made a solemn promise to myself to not operate an air circuit breaker anytime soon!
To give a small example, this is a test where I applied a small fault to a piece of switchgear with a minor manufacturing fault (deliberate), the piece of heat sensitive board to the front-left of the switchgear is the size and in the place where the operator would be when operating it.
View attachment 101428
View attachment 101429
View attachment 101430
View attachment 101431
View attachment 101432
View attachment 101433
Unfortunately although you can see the "operator" pushed back, the angle obscures the view - the material was burnt right through in places, indicating the operator could have suffered 3rd/4th degree burns to 75/40% of their body.
I think it is the "dependant operation" aspect, in other words unless you can and know how to make the damn thing operate VERY QUICKLY you get a serious arc-flash/arc-blast risk.P.S. And why must the OB3 NOT BE OPERATED? Is/was it defective like the above? All very interesting by the way.
People have been known to start opening them, halfway through closing them because they hear arcing.
What are those disc things all around the room. In fact, what is that room? @Julie. And, errr, I have made a solemn promise to myself to not operate an air circuit breaker anytime soon!
P.S. And why must the OB3 NOT BE OPERATED? Is/was it defective like the above? All very interesting by the way.
The red Yellow and blue busbars are the three phases we connected the equipment to, we could choose the voltage on those from 200V to 38kV depending upon the test requirements, the disks are insulators.
That is a test bay at a switchgear testing station, low - medium voltage, unfortunately I don't have photos of the other bays some of which go to high voltage (66kV+)
The OB3 operates like many of the era and is known as "dependant manual"
This means the speed of contact closure is completely dependent upon the operator, if you are hesitant and do it slowly or even stop and reverse, then the contacts will not make properly.
Switchgear is generally designed to close onto a fault, but opening a fault is not always required (switches), and when it is able to interrupt a fault (breaker), they sometimes use different contacts, and in any case they always need to follow the proper cycle from: contact made, contact separation, arc, arc control, then arc extinction then fully open.
Dependant manual interrupts this cycle.
As long as you make a swift closure, even on to a fault, the breaking cycle can complete safely.
As you may guess I worked at both a switchgear manufacturer and testing station , unfortunately I had to go out and investigate some incidents including a number where deaths had been involved.
I did attend one where an operator had started to close a switch (~11kV) designed in the late '40s manufactured in the 50s - so dependant manual, and realised he hadn't removed the earth links, so hesitated half way through and tried to open it.
5 out of the 6 people in the switchroom died, the one who lived was near the door managed to get out but was engulfed in the burning oil, it was horrific to be honest, one of the worst I investigated.
A YouTube search for “breaker failure” shows a tragic case of someone presumably winding out a switch under load. (Upsetting video - they don’t survive the massive explosion)
Wow @Julie. never realised what sort or work you did. Way past my pay grade and sounds absolutely fascinating. Plus your worked maths on 3P obviously way up there. Good for you. Nice to see a woman in such a place.
I think its safe to say that @Julie. Knows a bit about this electricity stuff.
During my career in the engineering and manufacturing industry's
I can only think of 4 Engineers that I consider really good in their field of work (proper engineers, not technicians that call themselves engineers)
3 of them are women, this is an unusual statistic because of how few women work in the engineering field compared to men.
Its hard to say without appearing patronising or sexist but well done to all the women who excel in the field of engineering because there have been and probably still are many obstacles they had to climb to get where they are today, that a man in the same position may not have encountered.
Yes, full respect deserved there!I think its safe to say that @Julie. Knows a bit about this electricity stuff.
I used to teach electronics many years back, and it was always disappointing to see how few women applied to study the degree in the first place as it represents a huge loss of potential talent that has gone elsewhere. That issue is a wider one for school and society to fix, alas.During my career in the engineering and manufacturing industry's
I can only think of 4 Engineers that I consider really good in their field of work (proper engineers, not technicians that call themselves engineers)
3 of them are women, this is an unusual statistic because of how few women work in the engineering field compared to men.
Its hard to say without appearing patronising or sexist but well done to all the women who excel in the field of engineering because there have been and probably still are many obstacles they had to climb to get where they are today, that a man in the same position may not have encountered.
You made me laugh out loud then!!As the saying goes, "For a woman to be considered half as good as a man, she has to be twice as good"
Fortunately, such a challenge is easily achieved
Just kidding, but it's kind of an open goal!
Actually that might have paid me more!I take it back, maybe you should have stayed as the receptionist, polished your nails, ignored the telephone, and worked part time as a comedian!!
![]()
Ouch..As the saying goes, "For a woman to be considered half as good as a man, she has to be twice as good"
Fortunately, such a challenge is easily achieved
Just kidding, but it's kind of an open goal!
Actually that might have paid me more!
Anyway @Julie. if you are ever stuck for a bit of cash I could probably use you for a bit of house-bashing when the pension days hit. Clearly you know a bit about electrics. In truth a captivating story. It is surprising the stories there are no doubt on here. Who knew?
![]()