Strange Monitoring behaviour | on ElectriciansForums

Discuss Strange Monitoring behaviour in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Joined
Sep 28, 2022
Messages
3
Reaction score
1
Location
Ashford
Hello all,

To avoid too techy questions, i am the consumer not he installer. I have raised the issue with my installer who is researching it, i'm posting here incase any of you have seen this before and have any suggestions. So , I have a hybrid inverter with storage attached and a regular PV inverter. Both go to a new consumer unit which is connected to the meter(grid) via a henley block (easier for the installer to run the cables down to the external meter housing than try and add inside. The CT clamp that goes to the hybrid inverter is on the grid side of the henley block and from what i can see the CT direction arrow is pointing towards to grid. The system works fine as far as i can tell, however... when the sun comes up and the PV inverter comes back on line (the hybrid is always on as its connected to batteries) the monitoring app (Solis app or solis cloud) show the generation from PV correctly (from both arrays), the battery charging correctly, BUT the draw from grid and house load is totally haywire. Generally it shows 0 load in house and huge loads going to the grid. When the sun goes down, all reverts to normal and it displays what seem to be reasonable figures. ie battery discharging, if U I put too many appliances on it'll draw from grid, battery and grid supply add up to load... I've drawn as best i can a logical diagram to show whats where.

[ElectriciansForums.net] Strange Monitoring behaviour

grateful for any suggestions / insights

cheers
Gareth
 
So spoke to Solis - this should work fine in their opinion, I need to do some trouble shooting, first step is to isolate both inverters, then load the system and the export meter should show a negative matching the load. Then take it from there. Will keep posting if it gets resolved.
 

Reply to Strange Monitoring behaviour in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

We had a similar call out and the issue was with the grid (which they admitted). Voltage was too high.
Replies
7
Views
635
If the batteries are charged and the house is taking little then the full production of the panels will be dumped into the grid. As you have set...
Replies
1
Views
611

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top