Hi All

Wondering if anyone can point me in the right direction regarding uk double sockets. Is there a reg or a British standard that manufactures have to stick with. As if my memory serves me right most double sockets will handle 20amps of load for long periods without causing any issue but is this for all sockets as standard. As currently have 1 of 2kw heater and 1 of 2kw sand blast machine plugged into a double socket. So pulling 17amps through the double socket just need to know if all sockets are rates for 13amp in total or is it 20amp s in total ?
 
My immediate response was to say "20A", as I believe type testing of the product involves taking 14A from one socket and 6A from the other (simultaneously) for 6? hours, which is probably where the 20A comes from.
But many basic twin 13A sockets now seem to be 'rated' (ie in their spec and stamped on the back) at 13A total.

However the spec for MK metalclad twin sockets says 13A per socket outlet, so the answer would be to fit one of those!
 
Are 13amp double sockets good for 17amps between the two outlets ?
If made by MK, yes!
[ElectriciansForums.net] Reg/standard for double socket
 
Last edited:
Ok no probs. Surely a standard double socket should be able to handle 17amps continuous load only 4amps above a 1gang socket which is rated for 13amp?
Not all 13A sockets are the same. They are all designed to meet the standard, but differences in design approach and the materials used mean some have better contacts (ie more robust connections) between the mating parts, the switch contacts, and the terminations for the cables. And some age better over time than others (as in don't develop poorer contact).
So I wouldn't venture to guess whether your brand new or 20 year old socket of unknown manufacture is up for the job or not.
If you're there all the time to keep an eye on it, just plug in your loads and see what happens - check regularly that it's not getting hot, especially after an hour or two. I don't mean a few degrees above ambient, but distinctly warm to the touch.
Quite useful to pull the plug out after a while and feel the pins! (NB if there's a suppressor in the equipment, this is a good way of sometimes getting a shock - maybe short L&N pins first!)

If you are in the workshop all the time it's on, that's perhaps less of an issue than leaving it on unattended!

Personally I'd be putting the heater on a different socket from the sand blasting machine, even if that meant wiring another (single?) socket into the ring somewhere.
 
Last edited:
IME the biggest problem with overheating sockets comes from one high load appliance approaching 13A, rather than two medium loads. The part most likely to overheat due to high combined load is the busbar serving the two switches, as this must take the dissipation of the two switch contacts. But it is much more common to see a burnt out socket contact where a dryer or similar high-load appliance has been used, than one with all female contacts intact but a burnt switch or busbar assembly (except where the wiring terminal has been left loose).

That said, @brianmoooore has the right approach for anything marginal on a double.
 

Reply to Reg/standard for double socket in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
  • Question
Result! :) Steve does a happy dance
    • Like
Replies
2
Views
1K
Depending on the size of the company, ie, has a H&S department or H&S. I'd just use the phrase that's it's not compliant with BS standards and...
Replies
48
Views
10K
OK, so as a quick update to this. I found a junction box (Wago Abox SL-2,5/4² # 80680701, see image) that looks like a great fit for my needs...
Replies
3
Views
4K
  • Question
I should I expanded more on the last sentence. Fusing is required, but this can be the fuse in a 13A plug, if the switch is connected to a single...
Replies
19
Views
21K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks