Posi joist wiring ref | on ElectriciansForums

Discuss Posi joist wiring ref in the UK Electrical Forum area at ElectriciansForums.net

J.C.E

-
Arms
Joined
Dec 2, 2010
Messages
832
Reaction score
165
Location
Earth
Evening

What ref method would you give t/e running the web of a posi joist?

100mm insulation below the posi joist then a MF and plasterboard ceiling below that

Cable not touch insulation

Cable touching:clipped to posi joist
[ElectriciansForums.net] Posi joist wiring ref
 
Essentially this is to determine the derating factor. I might say 103, although not surrounded by insulation of >100mm the UFH might cause the ambient temperature to be equivalent. Would need to know more about expected UFH temperature for derating first. What is the cable for sockets or lighting? But then if I found out the insulation below the UFH was such that it did not raise the ambient temperature it may be a different conclusion i.e.101. It does need a bit of thinking about from the idea do we use ref. method to derate or ambient temp. to further derate. Meaning a RFC would need to be done in 6mm² or worse, which aint happening. Needs more information I would say.
 
If there is UFH of the floor above, the thermal insulation should be at the top of the joists, keeping the void cool.

Why? Insulation between floors is normally fitted for acoustics rather than any thermal consideration, this is backed up by the specified double layer of acoustic plasterboard. So to achieve the best acoustic performance it would be at the bottom of the void tight against the plasterboard.
 

Reply to Posi joist wiring ref in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

  • Question
I would use the Switch & Load 16A - https://www.quickwire.co.uk/product/switch-load-16a/ Designed to do the same thing as the ceiling rose in...
Replies
5
Views
761
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
648

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top