Hi. I have very old underfloor heating with thermostats. I'd like to replace the thermostats with timer/thermostats if possible. The current (very old) ones have 2 red cables, 2 black and an earth. One of the red cables is live all the time, the other live when the thermostat kicks in. It appears to be mains voltage. Can anyone suggest a replacement thermosat with a built-in timer please? Many thanks.
 

Attachments

  • [ElectriciansForums.net] Replacement thermostat / timer
    20221107_153902.jpg
    200.1 KB · Views: 14
  • [ElectriciansForums.net] Replacement thermostat / timer
    20221107_153909.jpg
    302.2 KB · Views: 14
I imagine that old Satchwell stat is switching the electric UFH mat directly. I believe its switch contacts are rated at 16A, not that your mat is necessarily taking the full 16A!
I believe many modern UFH timer stats are designed for wet systems, where they switch the boiler or a valve with much lower current. So you would need to get one suitable for the load of your floor.
This sort of thing would do:

I've used one of these - good but I had one fail!
There must be others available with 16A contacts!
PS I'm assuming your black wires are actually neutral, I guess that's pretty likely, but worth checking if you have a meter.
 
Last edited:
I imagine that old Satchwell stat is switching the electric UFH mat directly. I believe its switch contacts are rated at 16A, not that your mat is necessarily taking the full 16A!
I believe many modern UFH timer stats are designed for wet systems, where they switch the boiler or a valve with much lower current. So you would need to get one suitable for the load of your floor.
This sort of thing would do:

I've used one of these - good but I had one fail!
There must be others available with 16A contacts!
PS I'm assuming your black wires are actually neutral, I guess that's pretty likely, but worth checking if you have a meter.
Many thanks for your reply which is very helpful. Is there a way to test the Amps needed ? I have a multimeter but limited expertise. Presumably if the Amp rating of the new one is insufficient it will just blow it ?
 
Match the contact spec of the existing. Quite honestly, just go for 16amp.
The stats may be directly switching the floor element, but many of the old systems used a contactor (aka mains relay). Is there a clunck from the electric cupboard when the heating kicks in?
 
Match the contact spec of the existing. Quite honestly, just go for 16amp.
The stats may be directly switching the floor element, but many of the old systems used a contactor (aka mains relay). Is there a clunck from the electric cupboard when the heating kicks in?
Do you think this one would do the job ?
 
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.
As an Amazon Associate Electricians Forums may earn a small commission from qualifying purchases.
I'm not so sure. It looks like the one from Amazon requires an external sensor to control the UFH.
It doesn't look like there is one present from your pics.

My mistake. Seems to have built in temp. sensor
 
I'm not so sure. It looks like the one from Amazon requires an external sensor to control the UFH.
It doesn't look like there is one present from your pics.
I'm pretty sure it has both an internal sensor (because of the slot in the front), and terminals for the external (underfloor) probe. And you select which you want in the setup menu (which would be the internal one in this case)
PS yes it does say built in air sensor in the features list.
PPS Sorry - I see you saw that yourself!
 

Reply to Replacement thermostat / timer in the Electric Underfloor Heating Wiring area at ElectriciansForums.net

Similar Threads

Is this a plumbing question or is your underfloor heating electric? It sounds like you have a mechanical problem, like a stuck solenoid /...
Replies
1
Views
1K
  • Question
You need a wi fi switch that is compatible with your switchbot thermostats. Remove the SCR, use the neutral and live to power the wifi switch, and...
Replies
8
Views
717
Try disconnecting the "central heating off" wire from terminal 2 and insulate it (eg Wago connector or choc block or similar) and tuck it out of...
2
Replies
32
Views
3K
As a "temporary" measure I went down a slightly different route. Nothing off the shelf appealed. In particular I wanted something with a good WAF...
Replies
7
Views
1K
I have a 2 year old 2000w electric panel heater. Devola Designer 2kW Smart Glass Panel Heater with Timer White - DVPW2000WH -...
Replies
0
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks