help with unvented cylinder, cobi with dual channel hive | on ElectriciansForums

Discuss help with unvented cylinder, cobi with dual channel hive in the Central Heating Systems area at ElectriciansForums.net

Joined
Nov 13, 2022
Messages
22
Reaction score
0
Location
north
hi need help with wiring this.
basically new build with combi boiler, unvented cylinder with dual channel hive
ive attached pics with the wiring diagram giving but im now using a hive instead
so ive altered it to what i think is correct
obviously ive never sleeved any or added earths in diagram as shown

the kit come pre wired with 2 zone valves and thats the way plumber has left it, so ive doubled zone 1 and 2 up in wiring centre with link from 12 to 6.
ive ran a 4core n earth to boiler from wiring centre. but only connected brown, blue, black to switch live out.
is this correct as ive alter the diagram as it was shown live from 15 to boiler, so i changed it and went from 1 to live in boiler to give it perm live.???

i also ran a 4core n earth to hive reciever into live,neutral, 3 and 4.
 

Attachments

  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_110606.jpg
    294.8 KB · Views: 17
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_110602.jpg
    272.2 KB · Views: 14
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_110316.jpg
    398.7 KB · Views: 12
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_101410.jpg
    446.7 KB · Views: 13
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_101403.jpg
    377.5 KB · Views: 14
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_101309.jpg
    372.3 KB · Views: 12
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_101306.jpg
    318.7 KB · Views: 13
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_101255.jpg
    320 KB · Views: 14
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_110616.jpg
    393.2 KB · Views: 11
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_134232[12736].jpg
    214.4 KB · Views: 12
  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    Scan.jpg
    342.3 KB · Views: 15
Something is very wrong there!

A combi boiler and an unvented cylinder just don't go together for a start.
What is the point of the unvented cylinder in this arrangement?

The plumber has joined the outgoing side of both valves together which is wrong.

You have bare copper links between the terminals of the joint box, they need to be insulated links.
 
With the number of pipes to the boiler it would suggest you have a system boiler and not a combi, also there would be no point in having an unvented cylinder with a combi
 
As per the clearly written warning label on the boiler terminals the supply to the external controls must be taken from terminal 2 and the switched live to the boiler connect to terminal 1.
 
Something is very wrong there!

A combi boiler and an unvented cylinder just don't go together for a start.
What is the point of the unvented cylinder in this arrangement?

The plumber has joined the outgoing side of both valves together which is wrong. One of those valves must be connected to the coil of the unvented cylinder.

You have bare copper links between the terminals of the joint box, they need to be insulated links.
sorry its a system boiler,
 
so why does this diagram only show 1 cable from outgoing side of boiler, do i need to use the grey aswell?
 

Attachments

  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    Screenshot_20221113-094440_Samsung Notes[12737].jpg
    350.3 KB · Views: 28
so why does this diagram only show 1 cable from outgoing side of boiler, do i need to use the grey aswell?

I would guess it is because that diagram is not supplied by the boiler manufacturer.

It looks like that diagram has been drawn by someone who doesn't understand what they are doing, where is it from?
 
I would guess it is because that diagram is not supplied by the boiler manufacturer.

It looks like that diagram has been drawn by someone who doesn't understand what they are doing, where is it from?
off a website.
so does the boiler need live, neutral,earth and 2 more cores or does its just need sw live from 15 in wiring centre,neutral,earth and then leave link in 1 and 2?
 
off a website.
so does the boiler need live, neutral,earth and 2 more cores or does its just need sw live from 15 in wiring centre,neutral,earth and then leave link in 1 and 2?

If it is from a random website and not from the boiler manufacturer then of course it isn't going to be correct for the specific boiler you are wiring.
It isn't even correct for the setup it shows.

The boiler needs a permanent supply, usually from a switched fused spur with a 3A fuse.
The boiler needs a signal from the external controls, this must be connected between terminals 1 and 2.
Terminal 2 is a 230V outgoing supply from the boiler to the external controls, terminal 1 is for a 230V switched live from the external controls.
The switched live at terminal 1 must come from the supply from terminal 2, this ensures that if the boilers internal fuse operates it cuts power to all parts of the boiler.

You can either connect terminals 1 and 2 to a volt-free output from the external controls or you can use terminal 2 to supply power to all of the external controls.
 
If it is from a random website and not from the boiler manufacturer then of course it isn't going to be correct for the specific boiler you are wiring.
It isn't even correct for the setup it shows.

The boiler needs a permanent supply, usually from a switched fused spur with a 3A fuse.
The boiler needs a signal from the external controls, this must be connected between terminals 1 and 2.
Terminal 2 is a 230V outgoing supply from the boiler to the external controls, terminal 1 is for a 230V switched live from the external controls.
The switched live at terminal 1 must come from the supply from terminal 2, this ensures that if the boilers internal fuse operates it cuts power to all parts of the boiler.

You can either connect terminals 1 and 2 to a volt-free output from the external controls or you can use terminal 2 to supply power to all of the external controls.
so this is the maual with the unvented cylinder.
is shows terminal 15 to boiler,, to me thats not a permanent live.

so basically all i want to do is get rid of the controls they sent me and fit a dual channel hive.
can you alter the wiring and show me please
 

Attachments

  • [ElectriciansForums.net] help with unvented cylinder, cobi with dual channel hive
    20221113_110602.jpg
    272.2 KB · Views: 16
so this is the maual with the unvented cylinder.
is shows terminal 15 to boiler,, to me thats not a permanent live.

No, terminal 15 in that diagram is not a permanent live, it is a switched live to the boiler.
But note 3 of that diagram says quite clearly that this diagram is for a basic boiler, you do not have a basic boiler, you have a system boiler.
 
If that's a system boiler why are there two other pumps? What are they supposed to be doing and how are they supposed to be controlled?

No, terminal 15 in that diagram is not a permanent live, it is a switched live to the boiler.
But note 3 of that diagram says quite clearly that this diagram is for a basic boiler, you do not have a basic boiler, you have a system boiler.
but that came as akit from plumbers merchants, but it wouldnt matter what boiler it was terminal 15 would never go to boiler would it, so the diagram is crap anyways for any wiring
 

Reply to help with unvented cylinder, cobi with dual channel hive in the Central Heating Systems area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

Certainly is!! And another thing .......... On the old Hive receiver the relay common is a separate terminal, whereas on the new Hive presumably...
Replies
5
Views
358
That's just a standard timer switch. The 2 red wires to the timer are the switch contacts, the 2 blue wires are power to the clock. The 'orange'...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top