J

joehat

I've always assumed this rule was the same under slabs or concrete, not just under soil Ect.
Am I correct as the regulation doesn't state so that's why I assumed it.

The reason being, I've just gone and quoted a job and another (electrician!!) quoted a lot less, I asked how much Ect and how he was doing it and he said he would cut a cap below the slabs and run swa to the shed. ??
 
Agricultural and Horticultural Premises.
In selection and erection of wiring systems in relation to external influences 705.522 indicates depths required for buried cables.
notes 1 and 2. This is where the 600 mm and 1 metre come from. (in relation to vehicles and and mobile agricultural machines)
This is not conclusive.

Handy , you beat me to it , but I posted anyway.

Getting fed up of 3 mobile dropping out.
 
Last edited:
Well domestically with small swa circuits/submains, i will always try to clip it above ground as much as possible, i would omit rcd protection if the route is visible or buried sufficiently

if i have to bury it (avoiding high risk areas such as flower beds etc) and its not sufficiently deep, i normally just put tape above the cable run and rcd protect the swa cable

i think this is as sensible an approach as you can arrive at realistically, and is similiar to the regs with cabling buried in walls etc, if not a little safer as its obviously swa

anything serious then i would endevour to bury at an appropriate depth
 
As above, you have to be realistic. I agree regarding RCD protection and maybe the regs should take account of this the same way cables in walls are. If someone has gone through a cable planting a tree, then either it was planted in a stupid place, or, more likely, the installer didn't use his common sense. Either avoid such routes or bury it appropriately. If you quoted for burying at 450mm in every situation you would either not get the job or it would be impossible anyway.
 
I quoted to go round the fence instead,
It was a new build, fcu would have fed from ring to shed with 1 double outside and one in shed with a light and this would have been 10-12 meters or so, 2 meters to shed if went under slab Ect.

Quoted £200
4 hours £120
Materials £80

He told me the previous quote £130 all in !!
 
Last edited by a moderator:
I quoted to go round the fence instead,
It was a new build, fcu would have fed from ring to shed with 1 double outside and one in shed with a light and this would have been 10-12 meters or so, 2 meters to shed if went under slab Ect.

Quoted £200
4 hours £120
Materials £80

He told be the previous quoted £130 all in !!

Tell the customer that your price is staying, you're too cheap as it is in my opinion, and that there is a difference between a cheap job and a good value job. Let them know exactly what paperwork they should be expecting and wait for the call, either to take you on for the job or to mop up the mess afterwards.
 
Sounds like they are just trying it on anyway. Why would a customer ring you up and say that? most just make a decision and you either get the job or never hear anything in my experience.
 
Tell the customer that your price is staying, you're too cheap as it is in my opinion, and that there is a difference between a cheap job and a good value job. Let them know exactly what paperwork they should be expecting and wait for the call, either to take you on for the job or to mop up the mess afterwards.

Yep
I said I take no short cuts and it would be to a high standard with good quality materials not thin plastic sockets Ect Ect

His face was like [emoji15] yet he was in a new 3 bed house prob £200 grand.
 
I quoted to go round the fence instead,
It was a new build, fcu would have fed from ring to shed with 1 double outside and one in shed with a light and this would have been 10-12 meters or so, 2 meters to shed if went under slab Ect.

Quoted £200
4 hours £120
Materials £80

He told me the previous quote £130 all in !!

Cash most likely, no certs, etc
 
I always try to aim for a minimum of 450mm when doing runs in gardens etc, but when its under a path... 300mm

There’s more than BS5761 to consider. Building Regulations and any applicable Housing Regulations such as NHBC might be applicable.

Good practice guides recommend:
Domestic- soft landscaping >450-600mm
Domestic- hard landscaping >600mm
Roads & driveways >900mm
Agricultural land >1000mm
Warning tape should be laid >300-450 with a 150 space between tape and cable.
Cable should be laid on a sand bed with sand covering to 100mm.
Where the cable rises above ground it should be protected by a duct, conduit or other suitable mechanical protection.
 
There’s more than BS5761 to consider. Building Regulations and any applicable Housing Regulations such as NHBC might be applicable.

Good practice guides recommend:
Domestic- soft landscaping >450-600mm
Domestic- hard landscaping >600mm
Roads & driveways >900mm
Agricultural land >1000mm
Warning tape should be laid >300-450 with a 150 space between tape and cable.
Cable should be laid on a sand bed with sand covering to 100mm.
Where the cable rises above ground it should be protected by a duct, conduit or other suitable mechanical protection.
Don't think the OP got the job or probably given up after 6 years.
 
There’s more than BS5761 to consider. Building Regulations and any applicable Housing Regulations such as NHBC might be applicable.

Good practice guides recommend:
Domestic- soft landscaping >450-600mm
Domestic- hard landscaping >600mm
Roads & driveways >900mm
Agricultural land >1000mm
Warning tape should be laid >300-450 with a 150 space between tape and cable.
Cable should be laid on a sand bed with sand covering to 100mm.
Where the cable rises above ground it should be protected by a duct, conduit or other suitable mechanical protection.

Welcome to the forum mate.
As above, best to take note of the dates of the posts.
Still its a good reference for anyone doing a search in the future.
 

Attachments

  • [ElectriciansForums.net] 600mm swa cable depth rule
    NJUG Table.PNG
    189 KB · Views: 33

Reply to 600mm swa cable depth rule in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Sounds more positive.
Replies
8
Views
472
  • Question
wouldn't surprise me if we adopt this sooner or later...
Replies
7
Views
1K
  • Question
It’s all a bit confused as he originally says I read that as with supply removed he was picking up 230v. My concern is/was that as the house...
Replies
13
Views
3K
I see that point . I’m going to have to run a new cable into the meter then at my cost. more than likely as I’ve finished the job now
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks